Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Is possible to have neutral current harmonics evaluation in ION8650A?

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • Is possible to have neutral current harmonics evaluation in ION8650A?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Charles_Murison Champion
570
Mehran_Mehrnia
Mehran_Mehrnia Champion
201
Ramasamy_N
Ramasamy_N Champion
115
View All

Recommended Forums

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Start a Topic
Solved
Ezequiel-PROLUX
Ezequiel-PROLUX
Contributor

Posted: ‎2019-05-30 12:45 PM

0 Likes
4
2072
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-05-30 12:45 PM

Is possible to have neutral current harmonics evaluation in ION8650A?

Hi all!

 

Is possible to have neutral current harmonics evaluation in ION8650A?

 

If so, please give me a advice.

 

Thanks in advance!

Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2019-05-31 12:13 PM

0 Likes
0
2058
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-05-31 12:13 PM

Correct, calculation would have to be done for each individual harmonic. The meter already has per phase harmonic informaion, no additional modules required. The harmonic modules get information from modules that get information form modules etc that read signals directly connected to the meter so there is nothing for netural current directly. 

L4 Prime for Advanced metering and Utilities

See Answer In Context

Reply
Replies 4
Ezequiel-PROLUX
Ezequiel-PROLUX
Contributor

Posted: ‎2019-05-31 04:43 AM . Last Modified: ‎2022-10-19 02:55 AM

0 Likes
0
2067
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-05-31 04:43 AM

I found this topic that helps with calculating the module of neutral current:

https://community.se.com/t5/Power-Metering/True-RMS-current-for-neutral/m-p/23269#M68

But I can't put that calculated value into the FFT module for I4. So I could have the harmonic evaluation from it. The I4 used is always zero and I can't change the input of the FFT.

Reply
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2019-05-31 09:50 AM

0 Likes
2
2066
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-05-31 09:50 AM

The process described in the KB is on a per-harmonic basis. There is no I4 input to the meter to feed into FFT. 

The ION8650 meter already comes with the modules already in the template.

L4 Prime for Advanced metering and Utilities
Reply
Ezequiel-PROLUX
Ezequiel-PROLUX
Contributor

Posted: ‎2019-05-31 10:12 AM

0 Likes
1
2063
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-05-31 10:12 AM

Hi Charles!

 

Thanks for the input.

 

So that calculation should be done for each individual harmonic, is what you mean?

 

And about the modules that you said ION8650 already have, you  mean the individual per phase harmonics,  coming from the HME (Harmonics Measurement) ? Because for neutral individual current I didn't find any  module...

Reply
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2019-05-31 12:13 PM

0 Likes
0
2059
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-05-31 12:13 PM

Correct, calculation would have to be done for each individual harmonic. The meter already has per phase harmonic informaion, no additional modules required. The harmonic modules get information from modules that get information form modules etc that read signals directly connected to the meter so there is nothing for netural current directly. 

L4 Prime for Advanced metering and Utilities
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore