Intermittent RS485 Communication Loss in EM6436H Energy Meters

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • Intermittent RS485 Communication Loss in EM6436H Energy Meters
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Picard Charles_Murison Picard
495
Ramasamy_N
Captain Ramasamy_N Captain
115
Mehran_Mehrnia
Captain Mehran_Mehrnia Captain
95
Robert_Lee
Admiral Robert_Lee Admiral
92
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Solved
Dineeesh
Dineeesh
Cadet

Posted: ‎2025-05-10 10:22 PM

0 Likes
2
386
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-05-10 10:22 PM

Intermittent RS485 Communication Loss in EM6436H Energy Meters

We have installed 24 EM6436H energy meters connected in a serial loop via RS485 for data acquisition. Occasionally, some meters randomly go offline. The issue is temporarily resolved by disconnecting and reconnecting the auxiliary power supply. However, this workaround only restores functionality for a few days before the meters go offline again.

 

 

We are seeking a permanent solution to address this recurring communication issue.

Labels
  • Labels:
  • Did you know
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Mehran_Mehrnia
Captain Mehran_Mehrnia Captain
Captain

Posted: ‎2025-05-12 08:58 AM

0 Likes
0
343
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-05-12 08:58 AM

Hi @Dineeesh 

 

As Charles mentioned, for further assistance, please reach out to the local tech support team.

Here are also some possible causes of the issue:

1- In Daisy chain wiring, please ensure Straight-line topology only. Loop or ring topology is not supported.

2- Since there are many devices, improper termination or biasing resistors can cause signal reflections or idle line voltage drift, leading to communication errors. 

To terminate a series, it is recommended to use a 120 W / 0.5 W resistor.
2- Long cable runs or poor shielding can introduce noise.
3- Please ensure all meters have unique Modbus addresses, and the same baud rate, parity, and stop bits across all devices and the master.

 

Best Regards,

-Mehran

L3 Expert Advanced metering

See Answer In Context

Reply
Replies 2
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2025-05-12 08:37 AM

0 Likes
0
345
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-05-12 08:37 AM

Hello @Dineeesh ,

 

I would strongly recommend you reach out to your local technical support, se.com-> support->contact center -> Help and Contact Center.

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Reply
Mehran_Mehrnia
Captain Mehran_Mehrnia Captain
Captain

Posted: ‎2025-05-12 08:58 AM

0 Likes
0
344
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-05-12 08:58 AM

Hi @Dineeesh 

 

As Charles mentioned, for further assistance, please reach out to the local tech support team.

Here are also some possible causes of the issue:

1- In Daisy chain wiring, please ensure Straight-line topology only. Loop or ring topology is not supported.

2- Since there are many devices, improper termination or biasing resistors can cause signal reflections or idle line voltage drift, leading to communication errors. 

To terminate a series, it is recommended to use a 120 W / 0.5 W resistor.
2- Long cable runs or poor shielding can introduce noise.
3- Please ensure all meters have unique Modbus addresses, and the same baud rate, parity, and stop bits across all devices and the master.

 

Best Regards,

-Mehran

L3 Expert Advanced metering

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of