Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

ION9000 v3.0.0 modbus comms

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • ION9000 v3.0.0 modbus comms
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Charles_Murison Champion
582
Mehran_Mehrnia
Mehran_Mehrnia Champion
217
Ramasamy_N
Ramasamy_N Champion
117
View All

Recommended Forums

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Start a Topic
Solved
ShaunTaylor
ShaunTaylor Contributor
Contributor

Posted: ‎2021-10-22 05:07 AM

0 Likes
6
3435
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-10-22 05:07 AM

ION9000 v3.0.0 modbus comms

Hi,

We are communicating from PME to 5x ION9000 meters over ethernet. On loss of voltage phases, the meters remain powered as they should, and comms to PME keeps working as it should, 

 

These meters are also communicating to SCADA over modbus.

 

4 of the meters are firmware v2.2.1, and on loss of phase voltage, the modbus comms continues to the SCADA as expected. 

 

However...

 

1 of the meters is firmware 3.0.0, and on loss of voltage, the modbus comms drops out to the SCADA.

 

All 5 continue to communicate to PME over ION. All meters remain fully powered up.

 

My question is whether there has been any cyber enhancements or bugs that may be causing the modbus comms to drop on loss of phase voltage? Anyone experience this? Is there a fix/setting?

 

We're doing further investigating on site but any suggestions are welcome.

 

 

Labels
  • Labels:
  • ION9000
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2021-11-15 10:59 AM . Last Modified: ‎2022-10-19 01:17 AM

1 Like
0
3206
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-11-15 10:59 AM

Hello @ShaunTaylor  and @sesa28787_bridg 

 

Please see https://community.se.com/t5/Metering-Power-Quality/New-Firmware-version-3-1-0-for-Advanced-Meters-is... for more information on V3.1.0 release.

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities

See Answer In Context

Tags (1)
  • Tags:
  • english
Reply
Replies 6
Tom_Stevenson
Tom_Stevenson Champion
Champion

Posted: ‎2021-10-22 08:25 AM . Last Modified: ‎2022-10-19 01:20 AM

1 Like
5
3429
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-10-22 08:25 AM

Hi Shaun - there is a chance that what you are seeing is described in this post.  There is an upcoming firmware release that addresses it in the case that it is, but the post provides a few workarounds to try in the near-term.

 

https://community.se.com/t5/Metering-Power-Quality/The-Value-of-quot-N-A-quot-register-of-PM8000-fir...

 

BR


Tom

Tags (1)
  • Tags:
  • english
Reply
ShaunTaylor
ShaunTaylor Contributor
Contributor

Posted: ‎2021-10-25 12:38 AM

0 Likes
4
3419
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-10-25 12:38 AM

Thanks Tom, it does sound like the issue could be caused by the same issue affecting the PM8000. I assume ION9000 shares the same framework issue. 

 

We'll do some more investigation on site, and keep an eye out for the f/w update.

 

Regards

Shaun

Tags (1)
  • Tags:
  • english
Reply
Tom_Stevenson
Tom_Stevenson Champion
Champion

Posted: ‎2021-10-25 08:24 AM

0 Likes
3
3412
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-10-25 08:24 AM

Hi Shaun - it is a firmware issue, but one of the workarounds is in the framework.  Firmware is shared across the ION9000/PM8000/ION7400, so typically when you see a version number 3.0.0 (ie) across these 3 families, you will find behaviour in common.  The same goes for ION frameworks - built and released as a family of them.

 

Tom

Tags (1)
  • Tags:
  • english
Reply
sesa28787_bridg
sesa28787_bridg Explorer
Explorer

Posted: ‎2021-10-27 08:22 AM

0 Likes
2
3375
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-10-27 08:22 AM

When do you expect a new firmware version to be released that addresses this issue? 

Tags (1)
  • Tags:
  • english
Reply
Tom_Stevenson
Tom_Stevenson Champion
Champion

Posted: ‎2021-10-27 08:34 AM

0 Likes
0
3372
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-10-27 08:34 AM

Hi Shaun - I will let @Daniel_Brandao comment on the official timing.

 

Thanks


Tom

Tags (1)
  • Tags:
  • english
Reply
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2021-11-15 10:59 AM . Last Modified: ‎2022-10-19 01:17 AM

1 Like
0
3206
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-11-15 10:59 AM

Hello @ShaunTaylor  and @sesa28787_bridg 

 

Please see https://community.se.com/t5/Metering-Power-Quality/New-Firmware-version-3-1-0-for-Advanced-Meters-is... for more information on V3.1.0 release.

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Tags (1)
  • Tags:
  • english
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore