Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Brand Logo
Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
close
  • Community Home
  • Forums
    • By Topic
    • By Topic
      EcoStruxure Building
      • Field Devices Forum
      • SmartConnector Forum
      EcoStruxure Power & Grid
      • Gateways and Energy Servers
      • Metering & Power Quality
      • Protection & Control
      APC UPS, Critical Power, Cooling and Racks
      • APC UPS Data Center & Enterprise Solutions Forum
      • APC UPS for Home and Office Forum
      EcoStruxure IT
      • EcoStruxure IT forum
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • EcoStruxure Geo SCADA Expert Forum
      • Remote Operations Forum
      Industrial Automation
      • Alliance System Integrators Forum
      • AVEVA Plant SCADA Forum
      • CPG Expert Forum DACH
      • EcoStruxure Automation Expert / IEC 61499 Forum
      • Fabrika ve Makina Otomasyonu Çözümleri
      • Harmony Control Customization Forum
      • Industrial Edge Computing Forum
      • Industry Automation and Control Forum
      • Korea Industrial Automation Forum
      • Machine Automation Forum
      • Modicon PAC Forum
      • PLC Club Indonesia
      Schneider Electric Wiser
      • Schneider Electric Wiser Forum
      Power Distribution IEC
      • Eldistribution & Fastighetsautomation
      • Elektrik Tasarım Dağıtım ve Uygulama Çözümleri
      • Paneelbouw & Energie Distributie
      • Power Distribution and Digital
      • Solutions for Motor Management
      • Specifiers Club ZA Forum
      • Електропроектанти България
      Power Distribution NEMA
      • Power Monitoring and Energy Automation NAM
      Power Distribution Software
      • EcoStruxure Power Design Forum
      • LayoutFAST User Group Forum
      Energy & Sustainability Services
      • Green Building Scoring and Certification Forum
      Light and Room Control
      • SpaceLogic C-Bus Forum
      Solutions for your Business
      • Solutions for your Business Forum
      Support
      • Ask the Community
  • Knowledge Center
    • Building Automation Knowledge Base
    • Remote Operations Devices Knowledge Base
    • Geo SCADA Knowledge Base
    • Industrial Automation How-to videos
    • Digital E-books
    • Success Stories Corner
    • EcoStruxure IT Help Center
  • Events & Webinars
    • All Events
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Partner Success
    • Process Automation Talks
    • Technology Partners
  • Ideas
    • EcoStruxure Building
      • EcoStruxure Building Advisor Ideas
      Remote Operations
      • EcoStruxure Geo SCADA Expert Ideas
      • Remote Operations Devices Ideas
      Industrial Automation
      • Modicon Ideas & new features
  • Blogs
    • By Topic
    • By Topic
      EcoStruxure Power & Grid
      • Backstage Access Resources
      EcoStruxure IT
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • Remote Operations Blog
      Industrial Automation
      • Industrie du Futur France
      • Industry 4.0 Blog
      Power Distribution NEMA
      • NEMA Power Foundations Blog
      Energy & Sustainability Services
      • Active Energy Management Blog
      Light and Room Control
      • KNX Blog
      Knowledge Center
      • Digital E-books
      • Geo SCADA Knowledge Base
      • Industrial Automation How-to videos
      • Remote Operations Devices Knowledge Base
      • Success Stories Corner
  • companyImpact

Important Announcement: Community Back to Full Functionality

Dear Members, we are thrilled to announce that our Community is back to full functionality and that posts publication is now enabled again! We appreciate your patience during the last weeks. Learn more about our Community Guidelines. Thank you, Schneider Electric Community Team.

ION9000 Logging capabilities

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Communities
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • ION9000 Logging capabilities
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Picard Charles_Murison Picard
292
Ramasamy_N
Commander Ramasamy_N Commander
75
DanL
Captain DanL Captain
71
Robert_Lee
Captain Robert_Lee Captain
67
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Solved
totocian91
totocian91
Cadet

Posted: ‎2021-06-24 02:02 AM

0 Likes
3
857
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-06-24 02:02 AM

ION9000 Logging capabilities

Hello,

We are looking to use ION9000 to do the following while performing a series of tests that includes voltage dips and changes in frequency:

 

  • Log high speed measurements (HS V rms, HS Irms, HS kW total, HS kVar total and HS frequency) at 2kHz (or 0.5 ms) intervals.
  • Pre-event logging (at least 10 sec), post-event logging (at least 60 sec)

 

 

My question are :

1) Is if its possible to perform these tests considering the pre and post event times and 

2) Would it be possible to record waveform data for the same period of time available in comtrade?

           

Thanks in advance,

Antonio

Labels
  • Labels:
  • ION9000
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2021-06-24 09:22 AM

2 Likes
2
846
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-06-24 09:22 AM

Hello @totocian91 ,

 

The ION9000 can log "burst data at 1/2 cycle rates, this would be 8.33 ms for 60Hz system or 10 ms for 50Hz systems. The meter cannot log any faster than this. As for how long you can log, this depends on the number of measurements logged and other settings in other places inside the meter.  

 

As for waveforms, this in part depends on the samples/per cycle setting, COMTRade has a limit of 75 records, If you set the formate to 32x54, you would need 12 pre-event records and 67 post-event records, this would be more than the 75 limit in the COMTRADE module. If the format was 16x96, the pre-event would be 7, post event would be 38 for a total of 46 waveforms for 1 event, this would be within the COMTRADE module's limit.

 

A configuration like this would consume most of the meter's internal Buffer memory, this is a special type of memory that is shared by all the data recorder, waveform recorder, eventlog and other modules inside the meter.

 

Regards,

Charles

 

L4 Prime for Advanced metering and Utilities

See Answer In Context

Tags (1)
  • Tags:
  • english
Reply
Replies 3
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2021-06-24 09:22 AM

2 Likes
2
847
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-06-24 09:22 AM

Hello @totocian91 ,

 

The ION9000 can log "burst data at 1/2 cycle rates, this would be 8.33 ms for 60Hz system or 10 ms for 50Hz systems. The meter cannot log any faster than this. As for how long you can log, this depends on the number of measurements logged and other settings in other places inside the meter.  

 

As for waveforms, this in part depends on the samples/per cycle setting, COMTRade has a limit of 75 records, If you set the formate to 32x54, you would need 12 pre-event records and 67 post-event records, this would be more than the 75 limit in the COMTRADE module. If the format was 16x96, the pre-event would be 7, post event would be 38 for a total of 46 waveforms for 1 event, this would be within the COMTRADE module's limit.

 

A configuration like this would consume most of the meter's internal Buffer memory, this is a special type of memory that is shared by all the data recorder, waveform recorder, eventlog and other modules inside the meter.

 

Regards,

Charles

 

L4 Prime for Advanced metering and Utilities
Tags (1)
  • Tags:
  • english
Reply
totocian91
totocian91
Cadet

Posted: ‎2021-06-27 07:13 PM

0 Likes
1
829
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-06-27 07:13 PM

Hello @Charles_Murison ,

 

Thanks for your prompt reply.

 

I believe I expressed incorrectly my query confusing sampling rate with logging speed.

 

What I am looking for is to log the behaviour of a power system for at least 10 secs prior and 60 secs post a triggered test (eg. voltage step, frequency step) at a minimum 2kHz sampling rate in 50Hz system.

 

As I understand, if I set the format to 32x54 I would need 10 pre-event records and 56 post-event records to capture the time window requested. However my sampling rate with this configuration would be 1.6kHz. 

 

Please correct me if I'm wrong and I would like to know if its possible to set the the meter to reach the 2kHz for that time frame. 

 

Thanks again

 

 

 

 

 

Tags (1)
  • Tags:
  • english
Reply
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2021-06-28 09:07 AM

0 Likes
0
816
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-06-28 09:07 AM

Hello @totocian91,

 

A bit of information to unpack here. The ION900 meter will sample inputs at 1024 samples per cycle. What I think you are asking about is storing information gathered by the meter. As you say, 32 samples per cycle is 1600 samples per second. The next highest recording format for waveform recording is 64x28, At this setting you would need 18 waveforms pre trigger, 108 waveforms post trigger. 

 

ION9000 cannot support this configuration.

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Tags (1)
  • Tags:
  • english
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Additional options
You do not have permission to remove this product association.
 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this forum after you log in or create your free account.