ION9000 Logging capabilities

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • ION9000 Logging capabilities
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Picard Charles_Murison Picard
478
Ramasamy_N
Captain Ramasamy_N Captain
113
Robert_Lee
Admiral Robert_Lee Admiral
92
Mehran_Mehrnia
Captain Mehran_Mehrnia Captain
89
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-24 02:02 AM

0 Likes
3
1839
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-06-24 02:02 AM

ION9000 Logging capabilities

Hello,

We are looking to use ION9000 to do the following while performing a series of tests that includes voltage dips and changes in frequency:

 

  • Log high speed measurements (HS V rms, HS Irms, HS kW total, HS kVar total and HS frequency) at 2kHz (or 0.5 ms) intervals.
  • Pre-event logging (at least 10 sec), post-event logging (at least 60 sec)

 

 

My question are :

1) Is if its possible to perform these tests considering the pre and post event times and 

2) Would it be possible to record waveform data for the same period of time available in comtrade?

           

Thanks in advance,

Antonio

Labels
  • Labels:
  • ION9000
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2021-06-24 09:22 AM

2 Likes
2
1828
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-06-24 09:22 AM

Hello @Anonymous user ,

 

The ION9000 can log "burst data at 1/2 cycle rates, this would be 8.33 ms for 60Hz system or 10 ms for 50Hz systems. The meter cannot log any faster than this. As for how long you can log, this depends on the number of measurements logged and other settings in other places inside the meter.  

 

As for waveforms, this in part depends on the samples/per cycle setting, COMTRade has a limit of 75 records, If you set the formate to 32x54, you would need 12 pre-event records and 67 post-event records, this would be more than the 75 limit in the COMTRADE module. If the format was 16x96, the pre-event would be 7, post event would be 38 for a total of 46 waveforms for 1 event, this would be within the COMTRADE module's limit.

 

A configuration like this would consume most of the meter's internal Buffer memory, this is a special type of memory that is shared by all the data recorder, waveform recorder, eventlog and other modules inside the meter.

 

Regards,

Charles

 

L4 Prime for Advanced metering and Utilities

See Answer In Context

Tags (1)
  • Tags:
  • english
Reply
Replies 3
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2021-06-24 09:22 AM

2 Likes
2
1829
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-06-24 09:22 AM

Hello @Anonymous user ,

 

The ION9000 can log "burst data at 1/2 cycle rates, this would be 8.33 ms for 60Hz system or 10 ms for 50Hz systems. The meter cannot log any faster than this. As for how long you can log, this depends on the number of measurements logged and other settings in other places inside the meter.  

 

As for waveforms, this in part depends on the samples/per cycle setting, COMTRade has a limit of 75 records, If you set the formate to 32x54, you would need 12 pre-event records and 67 post-event records, this would be more than the 75 limit in the COMTRADE module. If the format was 16x96, the pre-event would be 7, post event would be 38 for a total of 46 waveforms for 1 event, this would be within the COMTRADE module's limit.

 

A configuration like this would consume most of the meter's internal Buffer memory, this is a special type of memory that is shared by all the data recorder, waveform recorder, eventlog and other modules inside the meter.

 

Regards,

Charles

 

L4 Prime for Advanced metering and Utilities
Tags (1)
  • Tags:
  • english
Reply
Anonymous user
Not applicable

Posted: ‎2021-06-27 07:13 PM

0 Likes
1
1811
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-06-27 07:13 PM

Hello @Charles_Murison ,

 

Thanks for your prompt reply.

 

I believe I expressed incorrectly my query confusing sampling rate with logging speed.

 

What I am looking for is to log the behaviour of a power system for at least 10 secs prior and 60 secs post a triggered test (eg. voltage step, frequency step) at a minimum 2kHz sampling rate in 50Hz system.

 

As I understand, if I set the format to 32x54 I would need 10 pre-event records and 56 post-event records to capture the time window requested. However my sampling rate with this configuration would be 1.6kHz. 

 

Please correct me if I'm wrong and I would like to know if its possible to set the the meter to reach the 2kHz for that time frame. 

 

Thanks again

 

 

 

 

 

Tags (1)
  • Tags:
  • english
Reply
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2021-06-28 09:07 AM

0 Likes
0
1798
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-06-28 09:07 AM

Hello @Anonymous user,

 

A bit of information to unpack here. The ION900 meter will sample inputs at 1024 samples per cycle. What I think you are asking about is storing information gathered by the meter. As you say, 32 samples per cycle is 1600 samples per second. The next highest recording format for waveform recording is 64x28, At this setting you would need 18 waveforms pre trigger, 108 waveforms post trigger. 

 

ION9000 cannot support this configuration.

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Tags (1)
  • Tags:
  • english
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of