New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).
ION8650A Power Meter Module 1 second readings calculation
Metering & Power Quality
Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.
Search in
Improve your search experience:
Exact phraseβUse quotes " "(e.g., "error 404")
WildcardβUse * for partial words(e.g., build*, *tion)
AND / ORβCombine keywords(e.g., login AND error, login OR signβin)
Keep it shortβUse 2β3 relevant words, not full sentences
FiltersβNarrow results by section(Knowledge Base, Users, Products)
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
β2015-08-1107:17 AM
ION8650A Power Meter Module 1 second readings calculation
I am running the Voltage and Current values from the power meter module, amongst others, into the sliding window demand module to take an interval average. I'd really prefer to take the HS, but it won't let me because the swd is low speed. The question is, are the values out of the 1 second power meter module the value at that instant, or is that the average over the course of that second? Or maybe something else?
We are using these values in a power quality analysis application, and need average steady-state data that is sampled often.
Link copied. Please paste this link to share this article on your social media post.
β2015-08-1109:46 AM
The HS Power Meter Module provides one-cycle voltage/current RMS values, updated every half-cycle. The (1s) Power Meter Module provides one-second voltage/current RMS values, updated every second.
Put another way, the (1s) Power Meter Module effectively does an RMS aggregation of all the HS values that were measured during that second. So it does account for all measured samples during each second, although the algorithm is an RMS aggregation rather than a mathematical average.