Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

ION8650 High Speed Data Recording

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • ION8650 High Speed Data Recording
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Charles_Murison Champion
566
Mehran_Mehrnia
Mehran_Mehrnia Champion
194
Ramasamy_N
Ramasamy_N Champion
115
View All

Recommended Forums

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Start a Topic
Solved
Sepehr_Zarrabi
Sepehr_Zarrabi Troubleshooter
Troubleshooter

Posted: ‎2020-04-02 03:45 PM

0 Likes
3
2649
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-04-02 03:45 PM

ION8650 High Speed Data Recording

I have an application where we need to record Freq. and kW at 32 samples per second (not cycles). 

 

A Setpoint module will trigger the recording if the Frequency goes out of bounds. However, I cannot figure out if we can have a Data Recorder module log that fast. In the manual I see "HIGH SPEED CONTINUOUS" but I have not been able to figure out what that means.

 

1) Is it possible to record values at 32 samples per second.

2) The next part of the requirement is to also record an analog signal at the same rate (32 samples per second). Is the Analog Input module a high-speed module?

 

Thank you!

Tags (1)
  • Tags:
  • ion8650
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2020-04-02 04:48 PM

0 Likes
2
2645
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-04-02 04:48 PM

Hello Sepehr,

 

1) Yes the meter is able to record values at a rate of 32 per second (period of 0.03125 seconds). I did test this on a meter with periodic timer of 0.031. The meter is able to record this fast. Note that this was also setup with the enable being controlled as to not have meter need to worry about wearing out the lash memory. 

 

Second part is to log the freq and kW, the default module for this is the power meter module, however this is updated only once a second. The high speed module does update at high speed. There is a catch however when using this module for frequency. The frequency measurement at this rate is susceptible to hysteresis and you may see a jump/dip in the value. The 1 second update is great without any issue and meets all standards we say the meter meets. However the HS power meter module has no standards for 1/2 cycle updates.

 

Second question: "record an analog signal at the same rate " I am afraid I do not have a meter with the IO module that I can test the update rate with. 

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities

See Answer In Context

Reply
Replies 3
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2020-04-02 04:48 PM

0 Likes
2
2646
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-04-02 04:48 PM

Hello Sepehr,

 

1) Yes the meter is able to record values at a rate of 32 per second (period of 0.03125 seconds). I did test this on a meter with periodic timer of 0.031. The meter is able to record this fast. Note that this was also setup with the enable being controlled as to not have meter need to worry about wearing out the lash memory. 

 

Second part is to log the freq and kW, the default module for this is the power meter module, however this is updated only once a second. The high speed module does update at high speed. There is a catch however when using this module for frequency. The frequency measurement at this rate is susceptible to hysteresis and you may see a jump/dip in the value. The 1 second update is great without any issue and meets all standards we say the meter meets. However the HS power meter module has no standards for 1/2 cycle updates.

 

Second question: "record an analog signal at the same rate " I am afraid I do not have a meter with the IO module that I can test the update rate with. 

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Reply
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2020-04-02 04:55 PM

1 Like
0
2643
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-04-02 04:55 PM

Small correction, I was looking at wrong document, I do not see analog inputs for the ION8650. I do see digital but that is not what I believe you are looking for.

 

Charles

 

L4 Prime for Advanced metering and Utilities
Reply
Sepehr_Zarrabi
Sepehr_Zarrabi Troubleshooter
Troubleshooter

Posted: ‎2020-04-08 09:01 AM

1 Like
0
2627
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-04-08 09:01 AM

Thank you @Charles_Murison. 

 

I also found this bit of information about high-speed logging as it pertains to the LogMode register of the Data Recorder module: 

"For typical logging use, this register does not need to be modified. For continuous high-speed logging (> 1 record per 60 seconds), this register should be set to High Speed Continuous."

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore