We are using the modbus export module to write 1s poll values to a device
The problem that when there is a write failure, that failure goes to the meter event log
I need to disable these recording of these event log modbus export fault logs, only from modbus export
Link copied. Please paste this link to share this article on your social media post.
You have to stop reading if you want to write something.
It can be done using AND-OR module with pending state at the Modbus Export output to enable/disable the Modbus Import or Modbus Master Device module.
One of my project usng ION75X0 RTU reading ION6200 meter we were required to perform reset those ION6200 from the RTU while reading those meters using Modbus Master Device.
Link copied. Please paste this link to share this article on your social media post.
Hello,
The WriteNow pulsed while busy is a hard coded event in the meter with a priority of 30. There is no way to disable this event being written to the event log directly. However there is an indirect method.
There is the Meter's event log controller module "Cutoff" setup register, this can set what the minimum priority is required for an event to get saved to a log. This is a global parameter that will affect all modules. Only change this setup register if you understand all implications of making the change.
Refer to the ION Reference for more information.
Charles
Link copied. Please paste this link to share this article on your social media post.
You have to stop reading if you want to write something.
It can be done using AND-OR module with pending state at the Modbus Export output to enable/disable the Modbus Import or Modbus Master Device module.
One of my project usng ION75X0 RTU reading ION6200 meter we were required to perform reset those ION6200 from the RTU while reading those meters using Modbus Master Device.