ION8650 Event Log Modbus Export Busy

Metering & Power Quality

Collaborate with multiple experts and discuss various topics about Power Meters and Power Quality. From design & implementation to troubleshooting and more, get support from experts and share your experiences by subscribing to the Schneider Electric Exchange forum today.

Solved
erik_tavares_en
Lieutenant | EcoXpert Master Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master
0 Likes
2
201

ION8650 Event Log Modbus Export Busy

We are using the modbus export module to write 1s poll values ​​to a device

 

ION1.png

 

 

 

The problem that when there is a write failure, that failure goes to the meter event log

 

 

Event.PNG

 

 

I need to disable these recording of these event log modbus export fault logs, only from modbus export


Accepted Solutions
Yut
Captain
Captain
0 Likes
0
193

Re: ION8650 Event Log Modbus Export Busy

You have to stop reading if you want to write something.

It can be done using AND-OR module with pending state at the Modbus Export output to enable/disable the Modbus Import or Modbus Master Device module.

 

One of my project usng ION75X0 RTU reading ION6200 meter we were required to perform reset those ION6200 from the RTU while reading those meters using Modbus Master Device.

See Answer In Context

2 Replies 2
Charles_Murison
Picard Picard
Picard
0 Likes
0
199

Re: ION8650 Event Log Modbus Export Busy

Hello,

 

The WriteNow pulsed while busy is a hard coded event in the meter with a priority of 30. There is no way to disable this event being written to the event log directly. However there is an indirect method.

 

There is the Meter's event log controller module "Cutoff" setup register, this can set what the minimum priority is required for an event to get saved to a log. This is a global parameter that will affect all modules. Only change this setup register if you understand all implications of making the change.

 

Refer to the ION Reference for more information.

 

Charles

L4 Prime for Advanced metering and Utilities
Yut
Captain
Captain
0 Likes
0
194

Re: ION8650 Event Log Modbus Export Busy

You have to stop reading if you want to write something.

It can be done using AND-OR module with pending state at the Modbus Export output to enable/disable the Modbus Import or Modbus Master Device module.

 

One of my project usng ION75X0 RTU reading ION6200 meter we were required to perform reset those ION6200 from the RTU while reading those meters using Modbus Master Device.