Hi my friends:
Our ION8650 meter has the Disturbance Direction Detection (DDD) capability (at least with the new firmware), we have loaded the meter with the newest V407 template, there is no DDD module in the default template (ION7650 does have), I can recreate DDD using the way that ION7650 does, but before I do that, I want to know if there is a newer template that does include DDD, another thing I want to get some advise is if I can use the way ION7650 is using on the ION8650 meter.
Thanks,
Rongjun Yao
Link copied. Please paste this link to share this article on your social media post.
As of today there are no newer released versions.
Templates can be downloaded from the website (though I don't see the V407 template there).
** UPDATE: Newer versions of the default template are expected soon, and they now contain the DDD module for A and B feature sets