ION7650 Framework identification

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • ION7650 Framework identification
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Picard Charles_Murison Picard
477
Ramasamy_N
Captain Ramasamy_N Captain
113
Robert_Lee
Admiral Robert_Lee Admiral
92
Mehran_Mehrnia
Captain Mehran_Mehrnia Captain
85
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Solved
Anonymous user
Not applicable

Posted: ‎2017-03-22 06:55 AM

0 Likes
8
1344
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2017-03-22 06:55 AM

ION7650 Framework identification

Hi, is there any way of checking the firmware version of an ION7650 from the front screen ?

Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
sesa64419
sesa64419 Schneider Alumni (Retired)
Schneider Alumni (Retired)

Posted: ‎2017-03-23 07:36 AM

0 Likes
2
1270
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2017-03-23 07:36 AM

Hi Richard

Here is a link to the ION7650 framework downloads:

v360:

http://www.schneider-electric.com/en/download/document/ION7650_v360_Template/

and v370:

http://www.schneider-electric.com/en/download/document/ION7650_V370_Template/

they contain the different framework variations.

If you have an older 10MB logging memory ION7650 you may get a reduction in memory (down to 5MB) if you update to the fully loaded framework +PQ and + IEC 61850. Just updating to the +PQ should not impact logging memory.

cheers,

Alana

See Answer In Context

Reply
Replies 8
Anonymous user
Not applicable

Posted: ‎2017-03-22 07:01 AM

0 Likes
6
1270
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2017-03-22 07:01 AM

Yes, it should be available in the Name Plt (Name Plate Info) display screen.

Reply
Anonymous user
Not applicable

Posted: ‎2017-03-22 07:14 AM

0 Likes
5
1270
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2017-03-22 07:14 AM

Thanks, i see that but is that not the firmware, or is it one in the same ?

Reply
Anonymous user
Not applicable

Posted: ‎2017-03-22 07:25 AM

0 Likes
4
1270
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2017-03-22 07:25 AM

I'm not in front of a device but based on the User Guide is says you should see firmeware version and template version. They are two different references.

For example, we have Firmware version 374e installed with template 7650_FAC-PQ-61850_V3.6.0.0.0.

Reply
sesa64419
sesa64419 Schneider Alumni (Retired)
Schneider Alumni (Retired)

Posted: ‎2017-03-22 07:41 AM

0 Likes
0
1270
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2017-03-22 07:41 AM

You can view this information if you connect to your ION7650 using ION Setup. It is on the Template tab in the Setup Assistant, the firmware, serial number, current template and default (factory loaded) template.

Reply
Anonymous user
Not applicable

Posted: ‎2017-03-23 01:46 AM

0 Likes
3
1270
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2017-03-23 01:46 AM

Thanks, seems the meter has juts the FAC version installed, not the FAC-PQ, can we apply this, where do we download it from ?

Reply
sesa64419
sesa64419 Schneider Alumni (Retired)
Schneider Alumni (Retired)

Posted: ‎2017-03-23 07:36 AM

0 Likes
2
1271
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2017-03-23 07:36 AM

Hi Richard

Here is a link to the ION7650 framework downloads:

v360:

http://www.schneider-electric.com/en/download/document/ION7650_v360_Template/

and v370:

http://www.schneider-electric.com/en/download/document/ION7650_V370_Template/

they contain the different framework variations.

If you have an older 10MB logging memory ION7650 you may get a reduction in memory (down to 5MB) if you update to the fully loaded framework +PQ and + IEC 61850. Just updating to the +PQ should not impact logging memory.

cheers,

Alana

Reply
Anonymous user
Not applicable

Posted: ‎2017-03-23 09:45 AM

0 Likes
1
1270
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2017-03-23 09:45 AM

Alana, hi

Thanks for the help on this one, the meter shows this version as being in it when the client browses to it:

The client is asking for the meter to be IEC61000-4-30 Class A capable, so are we OK or do we need to apply the PQ framework, if we do then which version will work with the meter firmware ?

Is there a document that exists anywhere that shows which frameworks can coexist with which firmware and what functions (in brief) each framework performs ?

Cheers

Reply
sesa64419
sesa64419 Schneider Alumni (Retired)
Schneider Alumni (Retired)

Posted: ‎2017-03-23 10:54 AM

1 Like
0
1270
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2017-03-23 10:54 AM

Hi Richard

Good news -- the fact you have fw vers 400 means you have the new internal hardware on your meter, so the logging memory won't be impacted if you wanted IEC 61850.

We don't have documentation as to which frameworks work on which firmware, but a rule of thumb is that earlier frameworks should work with later firmware. It is the firmware that defines which ION modules that are available for use in the framework.

We do, however, have a document that talks about 4-30 and supported firmware/frameworks. You can get it from the Schneider website here:

http://www.schneider-electric.com/en/download/document/70072-0185/

If you have v400 firmware and you upgrade to the v360 or v370 PQ framework, you are compliant to class A edition 2.

Hope this helps,

Alana

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of