Hello Everyone
I have a question.about ION 7X50 firmware compatibility.
Firmwares from v366 to v373 (lower than v400) are supported by ION7650 meters with serial numbers that ends in -01 or -02 (i.e: PJ- 09XXAXXX-01 / PJ- 10XXAXXX-02 / MJ- 10XXBXXX-02)? Or will it be problems with internal hardware?
I would like you can help with this question.
Thank you
Farid
Link copied. Please paste this link to share this article on your social media post.
Hello Farid
Firmware lower than v400 will work on ION 7x50 meters with serial numbers ending in -04 or lower.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2019-08-08 01:35 PM
Link copied. Please paste this link to share this article on your social media post.
Thank you very much Charles_M
Best Regards