Welcome to the new Schneider Electric Community

It's your place to connect with experts and peers, get continuous support, and share knowledge.

  • Explore the new navigation for even easier access to your community.
  • Bookmark and use our new, easy-to-remember address (community.se.com).
  • Get ready for more content and an improved experience.

Contact SchneiderCommunity.Support@se.com if you have any questions.

Close
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
Send Invite Cancel
84570members
353842posts

ION7650-8800 voltage wiring in MV systems for EN50160

Metering & Power Quality

Collaborate with multiple experts and discuss various topics about Power Meters and Power Quality. From design & implementation to troubleshooting and more, get support from experts and share your experiences by subscribing to the Schneider Electric Exchange forum today.

sesa216946_brid
Schneider Alumni (Retired)
Schneider Alumni (Retired)
0 Likes
4
434

ION7650-8800 voltage wiring in MV systems for EN50160

I propose here a method we are using in Italy to allow ION meters with EN50160 framework to correctly detect and classify the voltage events when installed in MV systems.

EN50160 states that, for MV systems, all the voltage events have to be evaluated using line-to-line voltages. This method shows how to allow it even when the voltage measures are transduced by 3 PTs wired line-to-earth.

Has anyone already faced the same issue and has already found a different solution (maybe via framework programming)?

Of course, any comment or advice about our proposed solution in the attached file is welcome.

Thank you

Attachments
4 Replies 4
aaron_azzo_com_
Ensign
Ensign
0 Likes
1
325

Re: ION7650-8800 voltage wiring in MV systems for EN50160

Thanks for the proposed solution Francesco.

Currently we have a ION 7650 on a HV installation.  The L-L is 11kV (Delta), but the secondary on the PT's is 110V L-L (we had to use L-L to power the meter on the auxiliary, as L-N would damage it and not allow power up).  There are three PT's (primary and secondary are Wye), and we currently have the active side of each PT going to V1, V2, & V3 on the 7650.  The Installation Guide does not give any reference to a system that has three VT's (or PT's) that I can see, so is this installation suggestion best practice?  It makes sense in theory, but do we have the backing of Schneider to actuate this in the field?

JamesAZZO
Sisko | EcoXpert Master Sisko | EcoXpert Master
Sisko | EcoXpert Master
0 Likes
0
325

Re: ION7650-8800 voltage wiring in MV systems for EN50160

can you give Aaron any insight?

toddl_hexeis_co
Ensign
Ensign
0 Likes
1
325

Re: ION7650-8800 voltage wiring in MV systems for EN50160

We also come across this configuration of PT's for MV systems quite often.  It is a standard PT installation configuration for a lot of protection relays.  As it is much easier to use existing PT's for a retrofit MV installation, it would really help if Schneider provide a wiring diagram for the ION7650's that supports this PT configuration.  Would likely help us sell a few more ION7650's for existing sites as well.

JamesAZZO
Sisko | EcoXpert Master Sisko | EcoXpert Master
Sisko | EcoXpert Master
0 Likes
0
325

Re: ION7650-8800 voltage wiring in MV systems for EN50160

Is this factory supported ?