Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

ION7400 and PM8240 Memorie Size available for data recording

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • ION7400 and PM8240 Memorie Size available for data recording
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Charles_Murison Champion
571
Mehran_Mehrnia
Mehran_Mehrnia Champion
202
Ramasamy_N
Ramasamy_N Champion
115
View All

Recommended Forums

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2019-01-21 09:31 AM . Last Modified: ‎2019-04-05 02:16 PM

0 Likes
10
4415
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-01-21 09:31 AM

ION7400 and PM8240 Memorie Size available for data recording

Hello everybody,

 

It's a simple question, can you tell me how many MB are available for ION7400 and PM8240 meters to store data? I remember these devices had only 10 MB available for framework but I realize with new firmwares version (1.4.3) increased the capacity of logging onboard.

 

I read the "What’s new in the... firmware version 1.4.3" document for meters and this only said: "This firmware release introduces changes to the meter’s logging architecture to allow for the use of more onboard memory for logging". I don't have any meter phisically with me, but checking offline ION7400 and PM8240 meters these devices have 473 MB available for logging data.

 

Can you confirm this onboard log storage capacity for ION 7400 and PM8240 meters?

 

Best Regards

Farid Yauri

Tags (2)
  • Tags:
  • ION 7400
  • pm8000
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2019-04-04 09:02 AM

0 Likes
0
4378
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-04-04 09:02 AM

Currently still limited to 10 MB, under investigation.

L4 Prime for Advanced metering and Utilities

See Answer In Context

Reply
Replies 10
Robert_Lee
Robert_Lee Champion
Champion

Posted: ‎2019-01-23 12:22 PM

0 Likes
9
4407
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-01-23 12:22 PM

Latest available firmware has increased available logging to approx 334 Mb *but* individual logs are still restricted to the 10 Mb limitation presently.  We are investigating possible ways to raise the logging limit but this impacts device response times when searching large logs for specific records to the point software timeouts are occuring.

Reply
JamesAZZO
JamesAZZO
Leader

Posted: ‎2019-04-04 03:56 AM

0 Likes
1
4382
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-04-04 03:56 AM

Does ION 9000 have the same limit?

Reply
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2019-04-04 09:02 AM

0 Likes
0
4379
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-04-04 09:02 AM

Currently still limited to 10 MB, under investigation.

L4 Prime for Advanced metering and Utilities
Reply
Anonymous user
Not applicable

Posted: ‎2019-05-20 07:50 AM

0 Likes
6
4358
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-05-20 07:50 AM

Hi @Robert_Lee 

 

Could you tell me if you already have a solution with a new firmware version to access more memory?

 

Thanks for your kind attention.

 

regards

 

Miguel

Reply
Robert_Lee
Robert_Lee Champion
Champion

Posted: ‎2019-05-21 09:28 AM

1 Like
5
4355
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-05-21 09:28 AM

Engineering is still looking into ways to allow timely access to large data files within an acceptable time so presently firmware is still restricted to 10 MB per individual recorders. 

 

ION9000 allows over 1.6 Gb of log storage while ION7400 and PM8000 models still allow 340+ Mb of total logging memory.

 

Allowing storage of vasts amount of data in the device does NOT allow the transfer of the data in a timely manner to a PC so having on board device storage that permits large data capture without sufficient means to extract the data to PME will result in data loss anyway (i.e. capturing 100 Mb of data every few seconds but only able to transfer a few MB in that time).

Reply
Tom_Stevenson
Tom_Stevenson Champion
Champion

Posted: ‎2019-05-21 10:06 AM

0 Likes
4
4351
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-05-21 10:06 AM

Hi Miguel - we are interested in the specific application you are trying to accomplish?  Or specific requirements?


Thanks !

 

Tom

Reply
Anonymous user
Not applicable

Posted: ‎2019-06-13 05:49 PM

0 Likes
3
4337
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-06-13 05:49 PM

Hi Tom,

 

The query went by the following: In several projects the ION7400 meters have been supplied and the final client has not consulted the reason that if in the technical manual or brochure indicates a memory capacity of 512MB only 10MB of its memory can be accessed is more with the latest firmware version is observed that you have access as a display by ION Setup to about 345MB but in realization has the limitation of 10MB even.

Is this already a resuleto to access the 345MB or 512MB of memory in the meter?

 

regards

 

Miguel Huaccha

Reply
Tom_Stevenson
Tom_Stevenson Champion
Champion

Posted: ‎2019-06-13 10:20 PM

1 Like
2
4333
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-06-13 10:20 PM

Hi Miguel - there is 345 MB available on a given device for logging.  The restriction of 10MB is now just per data recorder, but you can have multiple data recorders on a meter.  The difference between 345 and 512 is to reserve space for other uses such as FTP space etc.  Does this clarify the question?

 

Thanks


Tom

Reply
Anonymous user
Not applicable

Posted: ‎2019-06-13 10:31 PM

0 Likes
1
4331
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-06-13 10:31 PM

Hi @Tom_Stevenson,

 

The case is as follows by a regulation in Peru is required the registration of power and frequency every 1 second, this implies a record of about or more than 5 million data in a single datarecord; that is why the query I understand by your answer that if we add several datarecord's that we can create we would arrive at the use of those 345MB?

 

The same has been replicated in an ION8650A or B and there were no problems!

 

Thanks

 

Miguel 

Reply
Anonymous user
Not applicable

Posted: ‎2019-06-18 10:33 AM

0 Likes
0
4320
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-06-18 10:33 AM

Hola Miguel,

 

You are correct, besides that if frequency is the main quantity you need to record, you can have a dedicated data recorder module only for that quantity, and it will have enough space for many records. You should also look into how long should the data be stored so you know exactly how many records you will need.

 

If you are having troubles to setup this meter configuration, reach out to the technical support team with a copy of the template you are working, and we will be able to help you.

 

Regards,

Fabricio

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore