ION7330 Counter rate
I'm working on an ION7330, I noticed that it does not have the storage module. I'm using a digital input to count events, I wonder if I can calculate how many events occurred over a period of time, a rate of events?
Link copied. Please paste this link to share this article on your social media post.
2016-11-2309:44 AM
Have you looked into the Arithmetic module, there is a calculate input (default unlinked is every second) if this input is linked the module only calculates when pulsed. In the formula there is a section for previous value. See ION reference for more information.