New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).
ION7330 Counter rate
Metering & Power Quality
Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.
Search in
Improve your search experience:
Exact phraseβUse quotes " "(e.g., "error 404")
WildcardβUse * for partial words(e.g., build*, *tion)
AND / ORβCombine keywords(e.g., login AND error, login OR signβin)
Keep it shortβUse 2β3 relevant words, not full sentences
FiltersβNarrow results by section(Knowledge Base, Users, Products)
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
β2016-11-2308:27 AM
ION7330 Counter rate
I'm working on an ION7330, I noticed that it does not have the storage module. I'm using a digital input to count events, I wonder if I can calculate how many events occurred over a period of time, a rate of events?
Link copied. Please paste this link to share this article on your social media post.
β2016-11-2309:44 AM
Have you looked into the Arithmetic module, there is a calculate input (default unlinked is every second) if this input is linked the module only calculates when pulsed. In the formula there is a section for previous value. See ION reference for more information.
Link copied. Please paste this link to share this article on your social media post.
β2016-11-2309:44 AM
Have you looked into the Arithmetic module, there is a calculate input (default unlinked is every second) if this input is linked the module only calculates when pulsed. In the formula there is a section for previous value. See ION reference for more information.