Ask our Experts
Didn't find what you are looking for? Ask our experts!
Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.
Search in
Link copied. Please paste this link to share this article on your social media post.
Hello!
Is it possible to use the IOM9000 or another power quality analyzer as a DLMS/COSEM to Modbus TCP/IP gateway? If so, could you provide instructions on how to do this? Thank you in advance!
Link copied. Please paste this link to share this article on your social media post.
ION9000, ION8650, ION7400 and ION8800 DLMS-enabled meters come preconfigured with frameworks that allow the meter to provide selected values to a DLMS master or Modbus Master, but these meters are not designed to translate or bridge between them.
Best Regards,
-Mehran
L3 Expert Advanced metering
Link copied. Please paste this link to share this article on your social media post.
ION9000, ION8650, ION7400 and ION8800 DLMS-enabled meters come preconfigured with frameworks that allow the meter to provide selected values to a DLMS master or Modbus Master, but these meters are not designed to translate or bridge between them.
Best Regards,
-Mehran
L3 Expert Advanced metering
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.