Hello!
Is it possible to use the IOM9000 or another power quality analyzer as a DLMS/COSEM to Modbus TCP/IP gateway? If so, could you provide instructions on how to do this? Thank you in advance!
Link copied. Please paste this link to share this article on your social media post.
ION9000, ION8650, ION7400 and ION8800 DLMS-enabled meters come preconfigured with frameworks that allow the meter to provide selected values to a DLMS master or Modbus Master, but these meters are not designed to translate or bridge between them.
Best Regards,
-Mehran
L3 Expert Advanced metering
Link copied. Please paste this link to share this article on your social media post.
ION9000, ION8650, ION7400 and ION8800 DLMS-enabled meters come preconfigured with frameworks that allow the meter to provide selected values to a DLMS master or Modbus Master, but these meters are not designed to translate or bridge between them.
Best Regards,
-Mehran
L3 Expert Advanced metering