New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).
ION Setup has trouble to set up CM4250 "Disturbance" alarms
Metering & Power Quality
Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.
Search in
Improve your search experience:
Exact phraseβUse quotes " "(e.g., "error 404")
WildcardβUse * for partial words(e.g., build*, *tion)
AND / ORβCombine keywords(e.g., login AND error, login OR signβin)
Keep it shortβUse 2β3 relevant words, not full sentences
FiltersβNarrow results by section(Knowledge Base, Users, Products)
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
β2016-07-1410:08 AM
ION Setup has trouble to set up CM4250 "Disturbance" alarms
I am using the latest ION 3.0.16182.01 from the Box folder to set up some CM4000 meter and there are still hicups in the "Disturbance" alarm configration: As shown below, for the "Swell Van/Swell Vbn/Swell Vcn" alarms, I checked the "Adaptive WFC untill Dropout" box for all three of them from the top to bottom, but when I was done with "Swell Vcn" and went back to "Swell Van" page, the screen automatically changed the opinion to "Adaptive WFC Full Duration". If I changed that one again back to "untill Dropout", the "Swell Vbn" one got changed to "Full Duration"...
The meter infor I am working on is below, and it is still relative new for a CM4000.
Would truely be appreciated if we can get this fixed. After all, CM4000 is probably the first bacth of powerlogic meters supported by ION Setup.
Link copied. Please paste this link to share this article on your social media post.
β2016-07-1411:40 AM
I've located the error in ION Setup (which I was incorrectly assuming how the firmware was using the bits needed to be asserted for the "Until Dropout" option was operating) and will be likely be available in the next available build in the next week or two.