I just tested a PM5330 and a PM5563 with ION Setup.
These are my comments:
- I was not able to change the log settings for the PM5330 (I think that we normally should be able to choose the interval and two parameters from a list of eight. See manual EAV15107-EN02 on page 75 ).
It is also not possible to change these settings on the device itself.
- I was not able to change the control mode of a Digital Output on the PM5330. Still I can change it on the device itself.
- I you want to change a CUSTOM alarm, you need first to tick enable and then to fill in the Setpoint Pickup value before you can use the pull down menus and before you can change the name. It looks like it is broken if you don't know that.
- I get errors if I change the channels of Data Log 1 for the PM5563. ("Unknown Command Result Error: 65535") Still the changes are made but the status will be set on disable. So you 'll need to enable it again.
Version ION Setup: 14155_03
Link copied. Please paste this link to share this article on your social media post.
HI Philippe, Instead of selecting PM5330 or PM5563 select the parent node i.e. PM5560, that should help you
Link copied. Please paste this link to share this article on your social media post.
I updated ION Setup to 3.0.14174.02.
Weird, I don't have PM5560, PM5561 and PM5563 as template.
Using the template PM5500 for the PM5330 does not give me the possibility to change the log settings.
Link copied. Please paste this link to share this article on your social media post.
Hi Philippe use this link to download the latest IONSet up https://schneider-electric.app.box.com/IonSetup/1/719403149
Link copied. Please paste this link to share this article on your social media post.
That is the version that I have.
Link copied. Please paste this link to share this article on your social media post.
I've noticed that in some instances, running a "upgrade" from a really older version sometimes doesn't properly install the needed files. If your still experiencing this issue where some models are not listed, then I recommend to uninstall the existing version via the control panel and then re-installing (you shouldn't lose your network setup but to be safe you should backup all your DAT files in the ION Setup config folder location).
Link copied. Please paste this link to share this article on your social media post.
Thank you! I'll try it.