ION Power Quality Analyser on a Backup Generator Supply

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • ION Power Quality Analyser on a Backup Generator Supply
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Picard Charles_Murison Picard
477
Ramasamy_N
Captain Ramasamy_N Captain
113
Robert_Lee
Admiral Robert_Lee Admiral
92
Mehran_Mehrnia
Captain Mehran_Mehrnia Captain
85
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Solved
conradvr_hexeis
Lieutenant JG conradvr_hexeis
Lieutenant JG

Posted: ‎2021-10-04 11:36 PM

1 Like
9
2417
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-10-04 11:36 PM

ION Power Quality Analyser on a Backup Generator Supply

Hi all,

 

When using an ION power quality analyser to monitor a Backup Generator MSB one issue is you will have extended 'voltage outages' by design, as the MSB bus is only live when the generator is running.  Hexeis is interested to know what others have done to the ION  Sag/Swell modules to enhance the reporting of Generator Sag/Swell/Outage events.

 

To date Hexeis has left the Sag/Swell module in the factory default setup i.e. always enabled.  This means that the voltage outages are long when running a Power Quality Summary report.  One idea is to disable the Sag/Swell module after an outage is longer than a set period, but the impact on the reports/alarms and SOE viewer will need to be tested.

 

Note that the IONs' control power is always connected to a UPS power supply.

 

Regards

Conrad

Labels
  • Labels:
  • ION7000
  • ION9000
  • PM8000
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2021-10-05 10:13 AM

1 Like
1
2412
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-10-05 10:13 AM

Hello @conradvr_hexeis ,

 

Be very careful with enabling/disabling modules when alarm is active.

 

When a meter detects a sag, the module with write an event to say sag/swell started. However if the module is disabled or a setting on the meter is changed, there is no sag/swell end event. PME is looking for this end event to determine if the alarm is currently active or not. So by disabling the module PME will get a sag start event however never see a sag end event and will have a constant active alarm in the view.

 

May have a better time in the report side of things to "ignore" sag/swell events with a duration greater than x. How to do this I do not know, could be a change to store procedure or new custom report or something else completely.

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities

See Answer In Context

Tags (1)
  • Tags:
  • english
Reply
DanL
Captain DanL Captain
Captain

Posted: ‎2021-10-06 09:18 AM

0 Likes
3
2387
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-10-06 09:18 AM

I am not aware of any meter-side negative effects resulting from disabling the SagSwell module via it's Enable setup register. This can be done via setup menu on the display or using ION protocol over communications.

The display's alarm entry for the SagSwell is moved from the "Active alarm" to the "Historical alarm" list (if it was previously active as described above)


The effects on any software or external reporting may be different if the software is keying off particular event log entry sequences that result from this configuration change.

See Answer In Context

Tags (1)
  • Tags:
  • english
Reply
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2021-10-07 11:29 AM

0 Likes
0
2351
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-10-07 11:29 AM

Hello Dan,

 

Sadly the issue is not meter side but in PME software. The software is queuing off entries in the meter's event log that are not created under certain conditions.

 

Regards,

Charles

 

L4 Prime for Advanced metering and Utilities

See Answer In Context

Tags (1)
  • Tags:
  • english
Reply
Replies 9
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2021-10-05 10:13 AM

1 Like
1
2413
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-10-05 10:13 AM

Hello @conradvr_hexeis ,

 

Be very careful with enabling/disabling modules when alarm is active.

 

When a meter detects a sag, the module with write an event to say sag/swell started. However if the module is disabled or a setting on the meter is changed, there is no sag/swell end event. PME is looking for this end event to determine if the alarm is currently active or not. So by disabling the module PME will get a sag start event however never see a sag end event and will have a constant active alarm in the view.

 

May have a better time in the report side of things to "ignore" sag/swell events with a duration greater than x. How to do this I do not know, could be a change to store procedure or new custom report or something else completely.

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Tags (1)
  • Tags:
  • english
Reply
conradvr_hexeis
Lieutenant JG conradvr_hexeis
Lieutenant JG

Posted: ‎2021-10-05 04:48 PM

0 Likes
0
2406
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-10-05 04:48 PM

Thanks Charles.  That was one of the side effects of using enable/disable that we wanted to check.  The other option we are planning to test is dynamic control the Nominal Voltage Input to force an end of event.

 

Man goal is to simply make the data more relevant and easy to use for the users so potentially some post processing as you have noted may be the answer.

 

Regards

Conrad

 

 

Tags (1)
  • Tags:
  • english
Reply
DanL
Captain DanL Captain
Captain

Posted: ‎2021-10-05 05:28 PM

1 Like
0
2401
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-10-05 05:28 PM

RE: "left the Sag/Swell module in the factory default setup i.e. always enabled"

just FYI, the factory default in the framework/template design was intentionally changed in all V2.0 and later frameworks (for the product lines you tagged) so that SagSwell (and all other PQ metrics requiring additional setup) are disabled.

Of course you need to be running a firmware with the same version or higher to use these frameworks (2018 Q4 and later)

Tags (1)
  • Tags:
  • english
Reply
Grant_IPACS
Commander Grant_IPACS
Commander

Posted: ‎2021-10-05 09:29 PM

0 Likes
5
2396
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-10-05 09:29 PM

@conradvr_hexeis i would love to know what the answer is as well, right now the only choices you have are about choosing what data you wish to ignore (and potentially miss the recording of) if you start / stop alarms & recording in framework.

 

Would be terrific if schneider could make up a recommended 'standby generator' framework for the purpose.

 

its like asking who you favourite kid is! (sort of)

 

 

Regards

Grant
Tags (1)
  • Tags:
  • english
Reply
Tom_Stevenson
Picard Tom_Stevenson Picard
Picard

Posted: ‎2021-10-06 08:31 AM

0 Likes
4
2392
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-10-06 08:31 AM

@DanL - do you know of any graceful means to exit the disturbance in the framework, or is this report side as @Charles_Murison suggests?


@Kevin_Huang 

Tags (1)
  • Tags:
  • english
Reply
DanL
Captain DanL Captain
Captain

Posted: ‎2021-10-06 09:18 AM

0 Likes
3
2388
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-10-06 09:18 AM

I am not aware of any meter-side negative effects resulting from disabling the SagSwell module via it's Enable setup register. This can be done via setup menu on the display or using ION protocol over communications.

The display's alarm entry for the SagSwell is moved from the "Active alarm" to the "Historical alarm" list (if it was previously active as described above)


The effects on any software or external reporting may be different if the software is keying off particular event log entry sequences that result from this configuration change.

Tags (1)
  • Tags:
  • english
Reply
Grant_IPACS
Commander Grant_IPACS
Commander

Posted: ‎2021-10-06 10:11 PM

0 Likes
1
2378
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-10-06 10:11 PM

@DanL so it it user entry 'enable / disable' via dialog only, or can we do it via a local Dig Input?

 

 

Regards

Grant
Tags (1)
  • Tags:
  • english
Reply
DanL
Captain DanL Captain
Captain

Posted: ‎2021-10-07 08:29 AM

0 Likes
0
2360
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-10-07 08:29 AM

The "SS1 Enable" setup register can be configured easily with the Setup menu on the meter display and with ION Setup configuration wizards.
If you leave the setup register set to "Enabled", you can still disable the module with a customized framework configuration to use the "Enable" input of the SagSwell module linked to any source you configure it for. NOTE: Neither the display nor the ION Setup configuration wizard can be used for custom configurations.

Tags (1)
  • Tags:
  • english
Reply
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2021-10-07 11:29 AM

0 Likes
0
2352
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-10-07 11:29 AM

Hello Dan,

 

Sadly the issue is not meter side but in PME software. The software is queuing off entries in the meter's event log that are not created under certain conditions.

 

Regards,

Charles

 

L4 Prime for Advanced metering and Utilities
Tags (1)
  • Tags:
  • english
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of