Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

We Value Your Feedback!
Could you please spare a few minutes to share your thoughts on Cloud Connected vs On-Premise Services. Your feedback can help us shape the future of services.
Learn more about the survey or Click here to Launch the survey
Schneider Electric Services Innovation Team!

ION 7650 dual modbus master gateway

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • ION 7650 dual modbus master gateway
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Picard Charles_Murison Picard
478
Ramasamy_N
Captain Ramasamy_N Captain
113
Robert_Lee
Admiral Robert_Lee Admiral
92
Mehran_Mehrnia
Captain Mehran_Mehrnia Captain
89
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Metering & Power Quality
Anonymous user
Not applicable

Posted: ‎2018-01-09 08:39 AM

1 Like
2
974
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2018-01-09 08:39 AM

ION 7650 dual modbus master gateway


          Is it possible to set an ION 7650 to act as a dual gateway for COM1 and COM2 using modbus master protocol? At the moment, there is 8 x PM5300 meters connected to COM1 using RS485 and 10 x PM5300 meters connected to COM2 using RS485, however I am only able to see one of those ports at a time, not both, depending on the serial connection I select as the gateway.

Reply
  • All forum topics
  • Previous Topic
  • Next Topic
Replies 2
sesa56307_bridg
Lieutenant JG sesa56307_bridg Lieutenant JG
Lieutenant JG

Posted: ‎2018-01-18 10:56 AM

0 Likes
1
918
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2018-01-18 10:56 AM

The ION7650 can certainly act as a Modbus Master on both COM1 and COM2 (retrieving data from downstream devices on the two serial loops, and making that data available in the ION framework for processing/logging).  But I believe the Modbus Gateway functionality (where a separate Modbus Master communicates using Ethernet through the ION7650 to downstream serial devices, in parallel with any Modbus Mastering by the meter) will only work on one serial port at a time, based on the "Modbus Gateway Connection" setup register.  Logically, the meter has no way to tell whether a Modbus Gateway request is for one port or the other, since the requests are just based on unit ID (which could be duplicated on the two serial loops).  So this is decided at configuration time.

If you need gateway-type functionality on both serial ports at the same time, you could consider using the EtherGate protocol instead, which permits a direct transfer of serial data to/from a downstream serial loop.  There are some caveats with EtherGate though (the Ethernet protocol is slightly different from Modbus TCP, the meter cannot Modbus Master that loop at the same time, and multiple master connections are not supported).  Please see the user guide for further information if this sounds interesting for your application.

Reply
Hal_Etheridge
Janeway Hal_Etheridge Janeway
Janeway

Posted: ‎2018-01-18 11:44 AM

0 Likes
0
919
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2018-01-18 11:44 AM

Generally you want to avoid using ModbusRTU protocol over Ethergate.  Due to how the ModbusRTU protocol is designed certain error conditions are not detectable by the modbus master and can result in malformed, corrupted or invalid data when used over Ethergate.  It will result in an increased error rate.  How much these issues will be present is dependent how a number of factors including the network latency and variability, which device types are present and the reliability of the devices themselves (among several others).  These issues may be acceptable tradeoffs for some simple installations.

A better solution would be to either:

- Combine the serial loops together (avoiding duplicate unit ids of course).  This will reduce performance due to the increase in the number of devices on the loop but if the loops were not saturated previously there may not be any visible performance decrease.

- Use a Modbus TCP to RTU gateway (like the new ComX devices or the old EGX series or even another 7650).

The second option will most likely give better overall performance but at increased cost.  The first is (possibly) cheaper if there are not that many devices and/or duplicate unit ids on the existing loops which will require reconfiguration of those devices.

Which option is better for you is dependent on your individual system configuration.

Reply
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of