Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

ION 7400 and PM8000 Modbus Map in ION Setup

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • ION 7400 and PM8000 Modbus Map in ION Setup
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Charles_Murison Champion
582
Mehran_Mehrnia
Mehran_Mehrnia Champion
216
Ramasamy_N
Ramasamy_N Champion
117
View All

Recommended Forums

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Start a Topic
Solved
kurtis_eisl_ca_
kurtis_eisl_ca_
Contributor

Posted: ‎2016-06-01 04:24 AM . Last Modified: ‎2020-04-22 01:25 AM

0 Likes
2
2123
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2016-06-01 04:24 AM

ION 7400 and PM8000 Modbus Map in ION Setup

Why Doesnt the Modbus Table show up in ION Setup as it does for the ION 7330 or ION 7550? Is it simply an oversight??

 

Labels
  • Labels:
  • ION Setup
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
sesa64419
sesa64419 Leader
Leader

Posted: ‎2016-06-01 07:32 AM

1 Like
1
2049
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2016-06-01 07:32 AM

Hi Kurtis

This is not an oversight.

The PM8000 and ION7400 have a different implementation of Modbus than for instance the ION7650. They do not use Modbus Slave modules to make the default Modbus map. Instead, they have a default map based on the power data model which uses Data Mapping modules.

You can download the default Modbus map here:

http://www.schneider-electric.com/ww/en/download/document/PM8000_Modbus_Map?showAsIframe=true

It is not recommended to manually modify the Data Mapping modules.

If you need to modify the Modbus data your meter provides, ION Setup is the best tool. When you click Edit (on the screen you have shown) you will get options of Default, Modified, Custom and Disabled.

Default: uses the default Modbus map (see download)

Modified: add more Modbus values to the default mapped values. This uses Modbus Slave modules.

Custom: default map is disabled and the registers are available to use in a custom map created with Modbus Slave modules. (this is intended for retrofit applications where you need to make the meter's Modbus data match with a previous device)

All of this information is described in the PM8000 user manual, 7EN02-0336-01 page 49-58 and in the ION7400 user manual.

cheers,

Alana

See Answer In Context

Reply
Replies 2
sesa64419
sesa64419 Leader
Leader

Posted: ‎2016-06-01 07:32 AM

1 Like
1
2049
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2016-06-01 07:32 AM

Hi Kurtis

This is not an oversight.

The PM8000 and ION7400 have a different implementation of Modbus than for instance the ION7650. They do not use Modbus Slave modules to make the default Modbus map. Instead, they have a default map based on the power data model which uses Data Mapping modules.

You can download the default Modbus map here:

http://www.schneider-electric.com/ww/en/download/document/PM8000_Modbus_Map?showAsIframe=true

It is not recommended to manually modify the Data Mapping modules.

If you need to modify the Modbus data your meter provides, ION Setup is the best tool. When you click Edit (on the screen you have shown) you will get options of Default, Modified, Custom and Disabled.

Default: uses the default Modbus map (see download)

Modified: add more Modbus values to the default mapped values. This uses Modbus Slave modules.

Custom: default map is disabled and the registers are available to use in a custom map created with Modbus Slave modules. (this is intended for retrofit applications where you need to make the meter's Modbus data match with a previous device)

All of this information is described in the PM8000 user manual, 7EN02-0336-01 page 49-58 and in the ION7400 user manual.

cheers,

Alana

Reply
kurtis_eisl_ca_
kurtis_eisl_ca_
Contributor

Posted: ‎2016-06-01 07:44 AM

0 Likes
0
2049
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2016-06-01 07:44 AM

Great Answer Thanks Alana!

Kurtis

Reply

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore