Hi All,
I am facing an issue with reading the RS485 data with the IEM 3255 Energy meter.
When I am trying to see the pf from the meter screen itself, it's showing me as -0.84 as shown in the image.Meter screen
However, when I'm trying to read from RS485 Bus, particularly, I am reading the register 0x0C0B, I am getting a response as " BF 8D 6F DA ".
This value, which is in IEEE754 floating point format, If I convert, I'm getting as ' -1.1049759 '.
Can anybody help me out with this problem?
The meter is connected in 3P3W configuration, all CT ratios are correct and even wiring type is correct.
Link copied. Please paste this link to share this article on your social media post.
Hi @Sabyasachi
As Charles mentioned correctly, iEM3000 series the same as PM5500 series perform a simple algorithm to the PF value then stores it in the PF register.
iEM3000 Power factor register format
Thank you.
Best Regards,
-Mehran
L3 Expert Tech Support Specialist
Link copied. Please paste this link to share this article on your social media post.
Hello @Sabyasachi
I believe the link below is for the PM5500 series but I believe the format is the same
https://www.productinfo.schneider-electric.com/pm5500/595e2aa946e0fb0001f715da/PM5500%20User%20Manua...
The PF value is calculated from the PF register value using the following formulas:
| Quadrant | PF range | PF register range | PF formula |
|---|---|---|---|
|
Quadrant 1 |
0 to +1 |
0 to +1 |
PF value = PF register value |
|
Quadrant 2 |
-1 to 0 |
-2 to -1 |
PF value = (-2) - (PF register value) |
|
Quadrant 3 |
0 to -1 |
-1 to 0 |
PF value = PF register value |
|
Quadrant 4 |
+1 to 0 |
+1 to +2 |
PF value = (+2) - (PF register value) |
Regards,
Charles
Link copied. Please paste this link to share this article on your social media post.
Hi @Sabyasachi
As Charles mentioned correctly, iEM3000 series the same as PM5500 series perform a simple algorithm to the PF value then stores it in the PF register.
iEM3000 Power factor register format
Thank you.
Best Regards,
-Mehran
L3 Expert Tech Support Specialist