Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

I cannot create a backup of an ION 7550 RTU through ION Setup

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • I cannot create a backup of an ION 7550 RTU through ION Setup
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Charles_Murison Champion
582
Mehran_Mehrnia
Mehran_Mehrnia Champion
216
Ramasamy_N
Ramasamy_N Champion
117
View All

Recommended Forums

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Start a Topic
Solved
RobertoDanielMejiaUbilla
RobertoDanielMejiaUbilla
Contributor

Posted: ‎2024-07-22 01:31 PM

0 Likes
2
1534
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-07-22 01:31 PM

I cannot create a backup of an ION 7550 RTU through ION Setup

I have three ION 7550 RTU meters connected and I cannot create a backup through ION Setup.
In the first one, when I connect, the setup assistant option does not appear, so I cannot access the meter information and know what firmware version it has.
With the others, the setup assistant window appears but when I make the backup and it is about to finish saving the template, Windows stops working and closes the ION Setup application. The latter have the same firmware version 3.71. I already repeated the process several times  and in all of them it is the same.
I have more meters connected such as ION9000, ION7650 and with all of them I can make backups, only with the ones that are RTU I have a problem
Any advice on what it could be?

Labels
  • Labels:
  • ION7000
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
RobertoDanielMejiaUbilla
RobertoDanielMejiaUbilla
Contributor

Posted: ‎2024-08-22 10:20 AM

0 Likes
0
1414
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-08-22 10:20 AM

Hi Charles.
I have managed to solve the setup assistant problem by following your steps.
For the other meters, when creating the backup and giving me the error, a 1KB file was created, I had tried to do it again but replacing the file and it didn't work, so I tried the backup again but now overwriting the damaged file and that solved the problem.
I was able to fix it but I still don't know what the root cause is, technical support is helping me with that.

See Answer In Context

Reply
Replies 2
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2024-07-22 01:55 PM

1 Like
1
1532
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-07-22 01:55 PM

Hello @RobertoDanielMejiaUbilla ,

For topic 1) "Setup assistant option does not appear" Can you right click on the RTU in the left panel and select properties, then select display tab. Choose an option to "hard code" what setup assistant ION Setup with use. Another thing to check is in the bottom left corner you may get a message about not being able to connect to the device. If you get that message it means ION Setup is not able to talk to the meter. Wil need to troubleshoot the communications. If you need help with that troubleshooting I suggest reaching out to your local technical support.

 

2) "DCF save to PC crashes ION Setup" - A little hard to troubleshoot this one over the forum. Do you have the latest version of ION Setup? I suggest reaching out to your local technical support for troubleshooting. They may want a copy of the system log.

With ION Setup closed, I suggest making a backup of or renaming SYSTEM.LOG. Then perform the activity that crashes ION Setup then include the file when you contact support.

 

Regards,

Charles

 

 

L4 Prime for Advanced metering and Utilities
Reply
RobertoDanielMejiaUbilla
RobertoDanielMejiaUbilla
Contributor

Posted: ‎2024-08-22 10:20 AM

0 Likes
0
1414
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-08-22 10:20 AM

Hi Charles.
I have managed to solve the setup assistant problem by following your steps.
For the other meters, when creating the backup and giving me the error, a 1KB file was created, I had tried to do it again but replacing the file and it didn't work, so I tried the backup again but now overwriting the damaged file and that solved the problem.
I was able to fix it but I still don't know what the root cause is, technical support is helping me with that.

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore