Posted: 2016-04-24 10:04 PM
Link copied. Please paste this link to share this article on your social media post.
One of my customer wanted the same so i install the following babel buster spx gateway which converts modbus rtu to SNMP
http://www.csimn.com/CSI_pages/BBSPX.html
BR
Genjua
Link copied. Please paste this link to share this article on your social media post.
Those meters are using Modbus RTU protocol seems to me that it is impossible to use SNMP, advice your customer to use Modbus RTU.
If there is some particular solution please share.
Posted: 2016-04-24 10:04 PM
Link copied. Please paste this link to share this article on your social media post.
One of my customer wanted the same so i install the following babel buster spx gateway which converts modbus rtu to SNMP
http://www.csimn.com/CSI_pages/BBSPX.html
BR
Genjua
Link copied. Please paste this link to share this article on your social media post.
Hi Waqas Mian thanks for your recommendation. Just one more thing, i need to install one per meter ? im looking the user guide and i cannot find information about qty of meters per gateway
best regards
Posted: 2016-04-25 11:43 PM
Link copied. Please paste this link to share this article on your social media post.
you can connect 32 daisy chain connected Modbus RTU Nodes with a single Babel Buster SPX Gateway.
Following link contain all the information related to gateway.
Modbus to SNMP Gateway: Babel Buster SPX
Also you can have a online demo of the gateway from the following link:
BR
Genjua