Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

How to assign PM8000 digital output to over / under voltage alarm ?

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • How to assign PM8000 digital output to over / under voltage alarm ?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Charles_Murison Champion
582
Mehran_Mehrnia
Mehran_Mehrnia Champion
217
Ramasamy_N
Ramasamy_N Champion
117
View All

Recommended Forums

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Metering & Power Quality
Start a Topic
sesa38559
sesa38559 Leader
Leader

Posted: ‎2017-05-26 10:58 AM

0 Likes
2
2376
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2017-05-26 10:58 AM

How to assign PM8000 digital output to over / under voltage alarm ?

Hi Folks ... am trying to operate an output when i have an under voltage / over voltage condition....

the meter is stand alone.... ( no PME ) can i use ION set up to link output with this alarm ?

Many thanks 🙂

Reply
  • All forum topics
  • Previous Topic
  • Next Topic
Replies 2
sesa64419
sesa64419 Leader
Leader

Posted: ‎2017-05-26 02:48 PM

0 Likes
1
2353
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2017-05-26 02:48 PM

Hi Patrick

Please refer to the PM8000 user manual located here:

http://www.schneider-electric.com/en/download/document/7EN02-0336/

You can set the source for the PM8000 digital outputs using ION Setup.

1) Open the setup assistant, select Onboard I/O (if using the onboard digital outputs) or Expansion modules (if using expansion I/O)

2) Select Source and click Edit. Navigate to the Relative Setpoint Module and select the desired phase (V1/V2/V3) and the desired condition (over or under) to transition the digital output. Click OK

3) Select Port and click Edit. This defines the physical port on the device. There is only one onboard digital output on the PM8000 so select Port D1 to select the onboard digital output port. Select a different port if using an expansion module.

4) Test and make sure everything works. >;-}

This is a bit limited as it only checks one phase, one condition. If you want to have your digital output to transition if any phase goes into either above or below, you could try out the following (remembering that I am not a frameworks expert!):

1) go into Advanced mode and make an And/Or module

2) connect up the And/Or Source Booleans to the outputs of the Relative Setpoint module's output Booleans for over/under

3) set the And/Or Mode to OR. With that setting the Result Boolean of the And/Or should go On if any of the Source Booleans are On.

4) Test and make sure everything works.

For more information about And/Or modules, Relative Setpoint modules and other ION modules on your meter, please refer to the ION Reference located here:

http://www.schneider-electric.com/en/download/document/7EN02-0290/

cheers,

Alana

Reply
sesa38559
sesa38559 Leader
Leader

Posted: ‎2017-05-28 11:03 AM

0 Likes
0
2353
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2017-05-28 11:03 AM

Thanks Alana :-).....

Sent from my iPhone

Reply

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore