New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).
Have you notice distorted values display on PM meters?
Metering & Power Quality
Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.
Search in
Improve your search experience:
Exact phrase→Use quotes " "(e.g., "error 404")
Wildcard→Use * for partial words(e.g., build*, *tion)
AND / OR→Combine keywords(e.g., login AND error, login OR sign‑in)
Keep it short→Use 2–3 relevant words, not full sentences
Filters→Narrow results by section(Knowledge Base, Users, Products)
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
2023-03-2705:33 AM
Have you notice distorted values display on PM meters?
Schneider electric PMxxxx and their efficient running rely largely on the connected Current Transformers, their installation and their calibration.
CTs are sensors sending electrical signal to the PMxxxx which then perform the calculation of your power quality and the subsequent value display.
Consequently, whether your CTs are not properly connected or calibrated, harmonics may be polluted, and value distortion could then be observed on your PMxxxx display.
But how can we prevent these disfunctions?
First of all, the CTs should be chosen according to wires and PMxxxx specification:
PM input current
PM accuracy class
Cable size and load
Voltage connection
Space between current transformers
Also note that common failure causes through the installation could be:
CTs connection to the PMxxxx
PMxxxx calibration
Degradation of the CTs*
Our range of Current Transformers:
Schneider Electric offers a large range of Current Transformers fully compatible with Schneider Electrics and Third-Party measurement devices. Our range is divided in two collection: