Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Fail to reset meter(PM5320) readings via Modbus TCP

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • Fail to reset meter(PM5320) readings via Modbus TCP
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Charles_Murison Champion
582
Mehran_Mehrnia
Mehran_Mehrnia Champion
216
Ramasamy_N
Ramasamy_N Champion
117
View All

Recommended Forums

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2022-06-10 12:47 AM

1 Like
7
8774
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-06-10 12:47 AM

Fail to reset meter(PM5320) readings via Modbus TCP

I am sending reset command (2009 & 2020) to the meter via Mod-bus TCP with reference to the FAQ. 

However, the meter have nothing happened and I receive [0,30659] when I try to check registers [5125-5126]. 

Can anyone tell me how to fix it?

 

Also, is there any command that I can reset all readings at once?

Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Ramasamy_N
Ramasamy_N Champion
Champion

Posted: ‎2022-06-16 11:02 PM

0 Likes
0
8598
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-06-16 11:02 PM

Hi @Anonymous user 

 

Please arrange remote session in team viewer or teams my email ID: ramasamy.narashimman@se.com

 

Regards, 

Ramasamy N

See Answer In Context

Tags (1)
  • Tags:
  • english
Reply
Replies 7
Ramasamy_N
Ramasamy_N Champion
Champion

Posted: ‎2022-06-13 04:49 AM

1 Like
6
8734
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-06-13 04:49 AM

Hello @Anonymous user 

 

Can you share the Wireshark traces when the commands 2009 & 2020 sent to the meter and response received form the meter for analysis?

 

You can use the ION setup to reset all (navigate to Meter resets -> Meter initialization) parameters. 

 

 

Regards, 

Ramasamy N

Attachments
Tags (1)
  • Tags:
  • english
Reply
Anonymous user
Not applicable

Posted: ‎2022-06-14 12:01 AM . Last Modified: ‎2022-06-14 01:55 AM

0 Likes
5
8705
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-06-14 12:01 AM

I have tried, but unable to get same fail result. However, the first register of reply are both 0.

@Ramasamy_N 

Attachments
modbus.txt
modbus_2.txt
Tags (1)
  • Tags:
  • english
Reply
Ramasamy_N
Ramasamy_N Champion
Champion

Posted: ‎2022-06-14 02:31 AM

0 Likes
4
8695
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-06-14 02:31 AM

Hi @Anonymous user 

 

The meter will accept the Modbus energy reset command if we follow the command structure as below, 

Register1 5000 = 2020

Register2 5001 = Semaphore received from the register 5680 

 

Can you please try once in ION setup and share the observation?

 

Regards, 

Ramasamy N

 

 

Tags (1)
  • Tags:
  • english
Reply
Anonymous user
Not applicable

Posted: ‎2022-06-16 08:39 PM

0 Likes
3
8613
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-06-16 08:39 PM

Hi @Ramasamy_N 

 

Both Min/Max and Energy are required reset.

I cannot execute reset via ION setup.

Attachments
Tags (1)
  • Tags:
  • english
Reply
Ramasamy_N
Ramasamy_N Champion
Champion

Posted: ‎2022-06-16 10:06 PM

0 Likes
2
8606
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-06-16 10:06 PM

Hi @Anonymous user 

 

You will get this error "unable to gain device setup access" if the meter HMI entered in to the setup menu. 

Keep the meter HMI in summary page and reset the energy from ION setup. 

 

Please make sure the device ID configured as 255. PM5320 device properties in ION setup.JPG

 

Regards, 

Ramasamy N

Tags (1)
  • Tags:
  • english
Reply
Anonymous user
Not applicable

Posted: ‎2022-06-16 10:59 PM

0 Likes
1
8600
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-06-16 10:59 PM

Hi @Ramasamy_N 

 

I wait for while and retry again but it return a unsuccessful.

Here attached is my print-screen and wire-shark captures.

Attachments
ION_0617a.txt
ION_0617b.txt
Tags (1)
  • Tags:
  • english
Reply
Ramasamy_N
Ramasamy_N Champion
Champion

Posted: ‎2022-06-16 11:02 PM

0 Likes
0
8598
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-06-16 11:02 PM

Hi @Anonymous user 

 

Please arrange remote session in team viewer or teams my email ID: ramasamy.narashimman@se.com

 

Regards, 

Ramasamy N

Tags (1)
  • Tags:
  • english
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore