Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

EDS files for PM5560 and PM5320

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • EDS files for PM5560 and PM5320
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Charles_Murison Champion
582
Mehran_Mehrnia
Mehran_Mehrnia Champion
217
Ramasamy_N
Ramasamy_N Champion
117
View All

Recommended Forums

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Start a Topic
Solved
ShaunTaylor
ShaunTaylor Contributor
Contributor

Posted: ‎2021-02-11 04:18 AM

0 Likes
7
8541
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-02-11 04:18 AM

EDS files for PM5560 and PM5320

Hi, my customer is needing to enable his Schneider PM5560 and PM5320 meters for comms with Rockwell ethernet protocol. For this they need the EDS files.

 

I have managed to find the EDS for the PM5560 in the latest firmware zip. However it appears to be missing from the latest PM5320 fimware zip. 

 

Could someone direct me to the file please?

 

Many thanks

Shaun

Labels
  • Labels:
  • PM5000
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Ramasamy_N
Ramasamy_N Champion
Champion

Posted: ‎2021-02-11 06:50 PM

3 Likes
4
8530
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-02-11 06:50 PM

Hello Shaun, 

 

PM5300 supports only the Modbus TCP and BACnet IP protocols. It does not supports Ethernet/IP protocol. 

We don't have the EDS file for PM5320. 

 

Regards, 

Ramasamy N

See Answer In Context

Tags (3)
  • Tags:
  • english
  • Hi
  • my customer is needing to enable his Schneider PM5560 and PM5320 meters for comms with Rockwell ethernet protocol. For this they need the EDS files.
Reply
Replies 7
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2021-02-11 09:08 AM

0 Likes
0
8535
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-02-11 09:08 AM

@Ramasamy_N , are you able to help Shaun?

 

Charles

 

L4 Prime for Advanced metering and Utilities
Tags (1)
  • Tags:
  • english
Reply
Ramasamy_N
Ramasamy_N Champion
Champion

Posted: ‎2021-02-11 06:50 PM

3 Likes
4
8530
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-02-11 06:50 PM

Hello Shaun, 

 

PM5300 supports only the Modbus TCP and BACnet IP protocols. It does not supports Ethernet/IP protocol. 

We don't have the EDS file for PM5320. 

 

Regards, 

Ramasamy N

Tags (3)
  • Tags:
  • english
  • Hi
  • my customer is needing to enable his Schneider PM5560 and PM5320 meters for comms with Rockwell ethernet protocol. For this they need the EDS files.
Reply
ShaunTaylor
ShaunTaylor Contributor
Contributor

Posted: ‎2021-02-12 12:27 AM

0 Likes
0
8527
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-02-12 12:27 AM

Thank you for the clarification Ramasamy. I had not spotted the distinction previously.

Tags (1)
  • Tags:
  • english
Reply
Anonymous user
Not applicable

Posted: ‎2022-11-25 02:18 AM

0 Likes
2
7695
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-11-25 02:18 AM

Hello Ramasamy, 

 

Do you know how the PM5560 generic module Assembly input on the Rocwell Logix tags should be set up? is it DINT, INT or SINT, or anything else?.  I use a generic module, and I can see the data is exchanged. (Implicit exchanges). But, it's not same as per actual data shown at the PM5560 parameter. i.e current. 

 

Any help will be appreciated. Thank you

 

Best regards

Aep

Tags (1)
  • Tags:
  • english
Reply
Ramasamy_N
Ramasamy_N Champion
Champion

Posted: ‎2022-11-25 03:53 AM

2 Likes
1
7688
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-11-25 03:53 AM

Hello Aep,

 

The generic module Assembly input to be set as REAL. 

Please refer the attached screenshot of configuration for more details. 

 

Regards,  

Attachments
PM556x with RS logix.docx
Tags (1)
  • Tags:
  • english
Reply
Anonymous user
Not applicable

Posted: ‎2022-11-25 07:05 PM

1 Like
0
7673
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-11-25 07:05 PM

Hello Ramasamy, 

Just changed the comm format to REAL, and then, bam! it's working. it showed the correct number. 🙂

so, thank you so much for your help!!

 

Best regards

Rahman

Tags (1)
  • Tags:
  • english
Reply
Patil8639
Patil8639
Explorer

Posted: ‎2026-08-19 08:15 AM

0 Likes
0
462
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2026-08-19 08:15 AM

We have rockwell plc with PM5560 meter on ethernet ip .i want eds file and mapping detail

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore