New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).
Download Events from a non ethernet based IN7550
Metering & Power Quality
Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.
Search in
Improve your search experience:
Exact phrase→Use quotes " "(e.g., "error 404")
Wildcard→Use * for partial words(e.g., build*, *tion)
AND / OR→Combine keywords(e.g., login AND error, login OR sign‑in)
Keep it short→Use 2–3 relevant words, not full sentences
Filters→Narrow results by section(Knowledge Base, Users, Products)
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
2024-06-0312:24 PM
Download Events from a non ethernet based IN7550
Is it possible to download power events recorded on *stand-alone non-ethernet based ION7550 direct to a laptop via Modbus Master such as an EGX150 or Panel Server.
No, the event log cannot be read using Modbus protocol. If able to connect directly to meter's serial port to a computer serial point you might be able to use ION Setup to read the data.
If going through a gateway, you would need a protocol agnostic gateway device or one that supports the ION protocol. EGX150 I believe supports ION protocol with some configuration changes. Panel Server I believe does not.
No, the event log cannot be read using Modbus protocol. If able to connect directly to meter's serial port to a computer serial point you might be able to use ION Setup to read the data.
If going through a gateway, you would need a protocol agnostic gateway device or one that supports the ION protocol. EGX150 I believe supports ION protocol with some configuration changes. Panel Server I believe does not.