Connecting to an ACM 3720 with ION Setup Via Modbus

Metering & Power Quality

Collaborate with multiple experts and discuss various topics about Power Meters and Power Quality. From design & implementation to troubleshooting and more, get support from experts and share your experiences by subscribing to the Schneider Electric Exchange forum today.

Solved
kurtis_eisl_ca_
Ensign
Ensign
0 Likes
2
406

Connecting to an ACM 3720 with ION Setup Via Modbus

End user is looking to setup a pulse output on an existing ACM3720 Power Meter. Can this be done via ION Setup by connecting to the ACM3720 over Modbus RTU through a Com'X?

 

Is there another way to setup the realy outputs to send a pulse?


Accepted Solutions
Charles_Murison
Picard Picard
Picard

Re: Connecting to an ACM 3720 with ION Setup Via Modbus

Hello Kurtis,

 

The ACM3720 meters are old. I found a document for some reference. https://www.se.com/ww/resources/sites/SCHNEIDER_ELECTRIC/content/live/FAQS/212000/FA212861/en_US/372...

 

https://www.se.com/resources/sites/SCHNEIDER_ELECTRIC/content/live/FAQS/212000/FA212772/en_US/Modbus...

 

It may be possible to program the relays but this is not something done via ION Setup. Starting on page 14 of the second link shows how to program the meter via modbus writes.

L4 Prime for Advanced metering and Utilities

See Answer In Context

kurtis_eisl_ca_
Ensign
Ensign
0 Likes
0
402

Re: Connecting to an ACM 3720 with ION Setup Via Modbus

Thanks Charles I have read both documents. As the ACM3720 is supported in ION Setup we had (hoped) that it could be ready through an Ethernet Gateway (Com'X) to program the relays; however it appears that ION Setup will only support in via PML protocol.

 

Thanks for the reply.

See Answer In Context

2 Replies 2
Charles_Murison
Picard Picard
Picard

Re: Connecting to an ACM 3720 with ION Setup Via Modbus

Hello Kurtis,

 

The ACM3720 meters are old. I found a document for some reference. https://www.se.com/ww/resources/sites/SCHNEIDER_ELECTRIC/content/live/FAQS/212000/FA212861/en_US/372...

 

https://www.se.com/resources/sites/SCHNEIDER_ELECTRIC/content/live/FAQS/212000/FA212772/en_US/Modbus...

 

It may be possible to program the relays but this is not something done via ION Setup. Starting on page 14 of the second link shows how to program the meter via modbus writes.

L4 Prime for Advanced metering and Utilities
kurtis_eisl_ca_
Ensign
Ensign
0 Likes
0
403

Re: Connecting to an ACM 3720 with ION Setup Via Modbus

Thanks Charles I have read both documents. As the ACM3720 is supported in ION Setup we had (hoped) that it could be ready through an Ethernet Gateway (Com'X) to program the relays; however it appears that ION Setup will only support in via PML protocol.

 

Thanks for the reply.