Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Compatibility between Rogowski Coil and PM5100

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • Compatibility between Rogowski Coil and PM5100
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Charles_Murison Champion
566
Mehran_Mehrnia
Mehran_Mehrnia Champion
194
Ramasamy_N
Ramasamy_N Champion
115
View All

Recommended Forums

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2019-12-23 03:03 AM . Last Modified: ‎2020-12-02 04:33 AM

0 Likes
4
8436
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-12-23 03:03 AM

Compatibility between Rogowski Coil and PM5100

#ask

This is my first post so bear with me if im doing some mistakes.

 

i have Schneider power meter 5100, and im planning to measure current using Rogowski Coil flexible CT

 

some seller said that PM5100 can't use Rogowski Coil because of compatibility issues and should use the normal CT

 

my question are, is it true that PM5100 can't use rogowski coil and if it's true, what type of CT are you guys recommending to me for my purpose above

 

thank you very much, any help is appreciated

Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BevanWeiss
BevanWeiss
Champion

Posted: ‎2019-12-23 11:22 AM . Last Modified: ‎2022-10-19 02:37 AM

0 Likes
1
8424
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-12-23 11:22 AM

Not the wrong section, but the wrong website.  'community.se.com'... it's for community exchange.  Not for 'Technical Support'.

 

If your amplifier complies with the other input specifications (i.e. it's ok with the input resistance of 0.3mOhm, and can provide for that burden power across the output range, then yes, it should be ok.

 

Typically more is better when it comes to CT currents.  You don't expect to be operating near your top end that often, so more resistance to noise at the bottom end is desirable.  More overall current = more resistance to induced noise at the bottom end.  Hence 5A CTs tend to be more common than 1A CTs.


Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..

See Answer In Context

Reply
Replies 4
BevanWeiss
BevanWeiss
Champion

Posted: ‎2019-12-23 03:24 AM

0 Likes
3
8432
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-12-23 03:24 AM

This is an exchange forum, for Schneider USERS, not for Schneider technical support.  You should contact your local Schneider Technical Support representative if you require a definitive answer from Schneider.

 

So the main issue here will be that the PM5100 will want a CT with a appreciable full scale current to it, something like 5A.

A Rogowski Coil on its own will not provide this.  However you can get amplifiers for these coils which will convert up to a 5A full scale for the Power Meter.  If you used such an 'amplifier', or some other means, to get the full scale up to the required setting for the Power Meter then it should work fine.


Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..
Reply
Anonymous user
Not applicable

Posted: ‎2019-12-23 04:18 AM

0 Likes
2
8427
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-12-23 04:18 AM

thank you for your reply

 
im sorry for posting in the wrong section. I have read the PM5100 specs and there's 1 / 5A in nominal current input
 
so if i use 1A "amplifier" for the rogowski coil, it should be working fine right ?
 
Attachments
Reply
BevanWeiss
BevanWeiss
Champion

Posted: ‎2019-12-23 11:22 AM . Last Modified: ‎2022-10-19 02:37 AM

0 Likes
1
8425
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-12-23 11:22 AM

Not the wrong section, but the wrong website.  'community.se.com'... it's for community exchange.  Not for 'Technical Support'.

 

If your amplifier complies with the other input specifications (i.e. it's ok with the input resistance of 0.3mOhm, and can provide for that burden power across the output range, then yes, it should be ok.

 

Typically more is better when it comes to CT currents.  You don't expect to be operating near your top end that often, so more resistance to noise at the bottom end is desirable.  More overall current = more resistance to induced noise at the bottom end.  Hence 5A CTs tend to be more common than 1A CTs.


Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..
Reply
Anonymous user
Not applicable

Posted: ‎2019-12-23 06:19 PM

1 Like
0
8418
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-12-23 06:19 PM

thanks for the reply

this is the specifications for what im planned to buy and install
based on your answer this product should be fine right ?

im planning to use 3 phase integrator 1A for the 3 rogowski coil, then the output from integrator goes to the PM5100 current input.

Attachments
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore