Important Announcement: Community Back to Full Functionality
Dear Members, we are thrilled to announce that our Community is back to full functionality and that posts publication is now enabled again! We appreciate your patience during the last weeks. Learn more about our Community Guidelines. Thank you, Schneider Electric Community Team.
Metering & Power Quality
Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Are you looking to store the value of kVA and kVAR at the time of peak kW?
If so, could the following work for you?
Create 2 store modules, one for kVA, one for kVAR, link the inputs to the desired measurement.
Connect the kW maximum module's trigger output to store module's store input.
Link copied. Please paste this link to share this article on your social media post.
Are you looking to store the value of kVA and kVAR at the time of peak kW?
If so, could the following work for you?
Create 2 store modules, one for kVA, one for kVAR, link the inputs to the desired measurement.
Connect the kW maximum module's trigger output to store module's store input.
Link copied. Please paste this link to share this article on your social media post.
Thanks
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.