Class 0.1S CT's for ION9000

Metering & Power Quality

Collaborate with multiple experts and discuss various topics about Power Meters and Power Quality. From design & implementation to troubleshooting and more, get support from experts and share your experiences by subscribing to the Schneider Electric Exchange forum today.

Solved
Grant_IPACS
Commander
Commander
0 Likes
2
480

Class 0.1S CT's for ION9000

Hi all,

We have a client possibly interested in ION9k upgrade from 8K.

 

I cant seem to find any Class 0.1S CT's here in Australia... given the standard is yet to be ratified, do they even exist yet, if so i would love to be sterred in the right direction.

 

Best Regards

 

Grant

Regards

Grant

Accepted Solutions
VictorMarincus
Sisko Sisko
Sisko
0 Likes
0
478

Re: Class 0.1S CT's for ION9000

Hi Grant,

You should look for optical CTs for 0.1S.

Areva used to have these a few years ago, but they are/were very expensive.

Regards,

Victor

See Answer In Context

2 Replies 2
VictorMarincus
Sisko Sisko
Sisko
0 Likes
0
479

Re: Class 0.1S CT's for ION9000

Hi Grant,

You should look for optical CTs for 0.1S.

Areva used to have these a few years ago, but they are/were very expensive.

Regards,

Victor

Yut
Captain
Captain
0 Likes
0
472

Re: Class 0.1S CT's for ION9000

My suggestion, in case you can't find 0.1 Class CT you may test those available CTs then put % of correction into the ITC Instrument Transformer Correction module pleas ION Reference for more detail.