Case Study Neutral conductor and transformer overload issues

Metering & Power Quality

Collaborate with multiple experts and discuss various topics about Power Meters and Power Quality. From design & implementation to troubleshooting and more, get support from experts and share your experiences by subscribing to the Schneider Electric Exchange forum today.

J_Meakins
Ensign Ensign
Ensign
0 Likes
0
272

Case Study Neutral conductor and transformer overload issues

Goal

To better understand the impact of harmonics on the 600 V bus duct and 2500 KVA transformer.

Solution

Use PowerLogic meters combined with StruxureWare Power Monitoring Expert software to calculate the true capacity of the facility’s transformer. This information helps to solve problems with neutral overloads and transformer heating.

Results

• New bus duct purchased with a neutral ampacity of 100%.

• Temporarily shared harmonic loading between two transformers

• Avoided millions of dollars in damaged product and lost sales.