Can the combination of HS power meter module's output register and set point module detect disturbance in a half cycle?

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • Can the combination of HS power meter module's output register and set point module detect disturbance in a half cycle?
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Picard Charles_Murison Picard
477
Ramasamy_N
Captain Ramasamy_N Captain
113
Robert_Lee
Admiral Robert_Lee Admiral
92
Mehran_Mehrnia
Captain Mehran_Mehrnia Captain
85
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Solved
Tomohiro-Okada
Lieutenant JG Tomohiro-Okada
Lieutenant JG

Posted: ‎2022-03-22 08:33 AM

0 Likes
7
2223
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-03-22 08:33 AM

Can the combination of HS power meter module's output register and set point module detect disturbance in a half cycle?

I have a question about detection of disturbance using ION7650's HS power meter module and setpoint module.

 

I know that HS power meter module can calculate half cycle RMS value of Voltage or Current, Frequency and so on.

I wonder if I connect the HS power meter module's output register to setpoint module's input register,

the combination of the modules  can detect disturbance in a half cycle(8.3ms or 10ms)?

or difference of the update cycles between the modules prevent it from detecting in a half cycle?

 

Do you have any idea?

 

Regards,

@Tomohiro-Okada 

 

Labels
  • Labels:
  • ION7000
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DanL
Captain DanL Captain
Captain

Posted: ‎2022-03-23 11:11 AM

3 Likes
3
2171
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-03-23 11:11 AM

The ION7650 Highspeed Power Meter module measurements are all measured over the previous cycle (1024 samples) and updated every half-cycle (512 samples). 

On the ION7650 the frequency measurement hardware is separate from the digital samples, so alignment of the Frequency output will be +/-0.5 cycles with the operation boundary.

Therefore input signal changes could take up to 1.5 cycles to propagate to the measurement outputs. The ION module processing is designed to complete ALL modules in less than 1 operating period (HighSpeed = 0.5cycles), so the SetPoint and DO modules will complete within another 0.5cycles.

The onboard solid-state digital outputs of the 7650 can have a few milliseconds of hardware response delay depending on the external load characteristics.

I would expect the total latency for this precise scenario to be between 10ms and 50ms.

 

NOTE: please see safety warnings in the documentation regarding use in control applications

See Answer In Context

Tags (1)
  • Tags:
  • english
Reply
Replies 7
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2022-03-22 01:36 PM

1 Like
6
2212
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-03-22 01:36 PM

Hello @Tomohiro-Okada 

 

The direct question is if possible to link the setpoint module to the output of a highspeed module and have the Setpoint module update at high speed. The answer is yes, it is possible to link.

 

The indirect question would be will this work and that is a larger question that will in part depend on what the desired outcome is.

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Tags (1)
  • Tags:
  • english
Reply
Tomohiro-Okada
Lieutenant JG Tomohiro-Okada
Lieutenant JG

Posted: ‎2022-03-23 03:32 AM

1 Like
5
2195
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-03-23 03:32 AM

Hello @Charles_Murison 

 

Thank you for your response.

 

I made example of specific HS power meter modules' connection.

(Please refer to the attached PDF document. I defined some setup registers' values, too.)

In this case, how long does it take to detect disturbance of frequency?

 

Regards,

Okada

Attachments
Tags (1)
  • Tags:
  • english
Reply
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2022-03-23 09:15 AM

0 Likes
0
2179
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-03-23 09:15 AM

Hello @Tomohiro-Okada ,

 

Yes the Setpoint module and digital output modules can be high speed but I do not know what the response time will be between input change (such as frequency) and the state change at the digital output.

 

Regards,

Charles

 

L4 Prime for Advanced metering and Utilities
Tags (1)
  • Tags:
  • english
Reply
DanL
Captain DanL Captain
Captain

Posted: ‎2022-03-23 11:11 AM

3 Likes
3
2172
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-03-23 11:11 AM

The ION7650 Highspeed Power Meter module measurements are all measured over the previous cycle (1024 samples) and updated every half-cycle (512 samples). 

On the ION7650 the frequency measurement hardware is separate from the digital samples, so alignment of the Frequency output will be +/-0.5 cycles with the operation boundary.

Therefore input signal changes could take up to 1.5 cycles to propagate to the measurement outputs. The ION module processing is designed to complete ALL modules in less than 1 operating period (HighSpeed = 0.5cycles), so the SetPoint and DO modules will complete within another 0.5cycles.

The onboard solid-state digital outputs of the 7650 can have a few milliseconds of hardware response delay depending on the external load characteristics.

I would expect the total latency for this precise scenario to be between 10ms and 50ms.

 

NOTE: please see safety warnings in the documentation regarding use in control applications

Tags (1)
  • Tags:
  • english
Reply
Tomohiro-Okada
Lieutenant JG Tomohiro-Okada
Lieutenant JG

Posted: ‎2022-03-23 05:59 PM

0 Likes
2
2162
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-03-23 05:59 PM

Hello @DanL,

 

Thank you for your specific answer!

 

I interpret your answer as follows

 

・Setpoint module can detect changes of the HS power meter module's output registers values

    (For examples, HS Vll avg, HS I avg, HS Freq, HS kW tot   *our customer concern about detection of these parameters)

    in a half cycle and if the values are greater than or less than the threshold values, 

    the Setpoint modules can notify it using output resisters without missing.

 

・Digital output modules can detect above output resisters(connected to force on of the output register )

   of Setpoint modules and output latching alarm.

 

Are these interpretations correct?

 

Thanks,

Okada

Tags (1)
  • Tags:
  • english
Reply
DanL
Captain DanL Captain
Captain

Posted: ‎2022-03-24 08:53 AM

2 Likes
1
2145
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-03-24 08:53 AM

Yes, I think that sounds correct.

 

Dan

Tags (1)
  • Tags:
  • english
Reply
Tomohiro-Okada
Lieutenant JG Tomohiro-Okada
Lieutenant JG

Posted: ‎2022-03-27 11:25 PM

0 Likes
0
2076
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-03-27 11:25 PM

Hello @DanL 

 

Thank you for your reply.

I understand about this.

 

Regards,

Okada

Tags (1)
  • Tags:
  • english
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of