I am not aware of any standard regarding sample rate. But harmonic calculation is tied directly to sample rate. The sample rate has to be at least twice +1 for the calculated harmonic. Thus you need a sample rate of 128 samples per cycle to determine harmonics through the 63rd. And of course, the higher the sample rate, the better the resolution of any waveforms captured.
Link copied. Please paste this link to share this article on your social media post.
Thanks. I will use this argument with consultant. Hopefully I do not need to teach them nyquist theorem first.