Metering & Power Quality
Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.
Posted: 2014-04-13 09:37 PM
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
I am not aware of any standard regarding sample rate. But harmonic calculation is tied directly to sample rate. The sample rate has to be at least twice +1 for the calculated harmonic. Thus you need a sample rate of 128 samples per cycle to determine harmonics through the 63rd. And of course, the higher the sample rate, the better the resolution of any waveforms captured.
Posted: 2014-04-14 06:31 PM
Link copied. Please paste this link to share this article on your social media post.
Thanks. I will use this argument with consultant. Hopefully I do not need to teach them nyquist theorem first.