New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).
Application Note - Correcting unbalanced current and voltage with PowerLogic AccuSine
Metering & Power Quality
Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.
Search in
Improve your search experience:
Exact phrase→Use quotes " "(e.g., "error 404")
Wildcard→Use * for partial words(e.g., build*, *tion)
AND / OR→Combine keywords(e.g., login AND error, login OR sign‑in)
Keep it short→Use 2–3 relevant words, not full sentences
Filters→Narrow results by section(Knowledge Base, Users, Products)
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
2025-05-1805:31 AM
Application Note - Correcting unbalanced current and voltage with PowerLogic AccuSine
Unbalance is listed as one of the possible power quality problems that are common in an electrical distribution system. Even so, it is often overlooked and can damage electrical components. This Application Note reviews the causes and effects, and describes possible solutions for, unbalanced current or voltage in electrical networks.
Voltage unbalance is probably the leading power quality problem that results in motor overheating and premature motor failure. If unbalanced voltages are detected, a thorough investigation should be undertaken to determine the cause. Energy and cost savings occur when corrective actions are taken.
Voltage Unbalance Energy Savings Example
Assume that the 100-hp motor tested as shown in Table 1 was fully loaded and operated for 8,000 hours per year (hrs/yr), with an unbalanced voltage of 2.5%. With energy priced at $0.08/kilowatt-hour (kWh), the annual energy and cost savings after corrective actions are taken are:
Annual Energy Savings = 100 hp x 0.746 kW/hp x 8,000 hrs/yr x (100/93 – 100/94.4) = 9,517 kWh Annual Cost Savings = 9,517 kWh x $0.08/kWh = $760
Overall savings may be much larger because an unbalanced supply voltage may power numerous motors and other electrical equipment.
Sreemant Roy Product Owner - Active Power Quality Solutions ( AccuSine & DVR's )