Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Join our "Ask Me About" community webinar on May 20th at 9 AM CET and 5 PM CET to explore cybersecurity and monitoring for Data Center and edge IT. Learn about market trends, cutting-edge technologies, and best practices from industry experts.
Register and secure your Critical IT infrastructure

Application Note - Correcting unbalanced current and voltage with PowerLogic AccuSine

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • Application Note - Correcting unbalanced current and voltage with PowerLogic AccuSine
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Picard Charles_Murison Picard
477
Ramasamy_N
Captain Ramasamy_N Captain
113
Robert_Lee
Admiral Robert_Lee Admiral
92
Mehran_Mehrnia
Captain Mehran_Mehrnia Captain
85
View All
Related Products
product field
PowerLogic
AccuSine PCS+

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Metering & Power Quality
Sreemant_Roy
Ensign Sreemant_Roy Ensign
Ensign

Posted: ‎2025-05-18 05:31 AM

1 Like
0
36
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-05-18 05:31 AM

Application Note - Correcting unbalanced current and voltage with PowerLogic AccuSine

Unbalance is listed as one of the possible power quality problems that are common in an electrical distribution system. Even so, it is often overlooked and can damage electrical components. This Application Note reviews the causes and effects, and describes possible solutions for, unbalanced current or voltage in electrical networks.

 

On a related topic check out this US DoE paper - Eliminate Voltage Unbalance

 

Voltage unbalance is probably the leading power quality problem that results in motor overheating and premature motor failure. If unbalanced voltages are detected, a thorough investigation should be undertaken to determine the cause. Energy and cost savings occur when corrective actions are taken.

 

Voltage Unbalance Energy Savings Example


Assume that the 100-hp motor tested as shown in Table 1 was fully loaded and operated for 8,000 hours per year (hrs/yr), with an unbalanced voltage of 2.5%. With energy priced at $0.08/kilowatt-hour (kWh), the annual energy and cost savings after corrective actions are taken are: 


Annual Energy Savings = 100 hp x 0.746 kW/hp x 8,000 hrs/yr x (100/93 – 100/94.4) = 9,517 kWh
Annual Cost Savings = 9,517 kWh x $0.08/kWh = $760


Overall savings may be much larger because an unbalanced supply voltage may power numerous motors and other electrical equipment.

Sreemant Roy
Product Owner - Active Power Quality Solutions ( AccuSine & DVR's )
  • Thumbnail of AccuSine PCS+
    PowerLogic
    AccuSine PCS+
View products (1)
Attachments
Labels
  • Labels:
  • Power Quality
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic
Replies 0
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of