Dear Community Members, We are currently experiencing a technical issue that is affecting the ability to create new posts. Our team is actively investigating the root cause and working to resolve it as quickly as possible. We apologize for the inconvenience and appreciate your patience. SE Community Team!
Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.
Search in
Link copied. Please paste this link to share this article on your social media post.
Hello All,
I'm attempting to alter the weighting of the Accusine SWP to increase the mitigation of 11th and 13th harmonic.
I need to target 3rd, 5th, 7th, 11th and 13th. Can I alter the application type to 35 (i.e. 32 + 3) to increase 11th to 90% and 13th
We have PQ monitors connected to the supply so we can detect resonance should it occur.
Link copied. Please paste this link to share this article on your social media post.
Hello ,
Yes you are free to change the profile if the current one is not the best adapted to you load. But it will improve the result only if with the existing profile (probably 0 if you let the default value) the h11 and h13 were blocked
Thierry B (L4 SWP support)