Hello Community,
We have a site with a 2.1% voltage unbalance, is there an unbalance voltage limit for Accusine
Link copied. Please paste this link to share this article on your social media post.
The calculation methods for these two values(power supply voltage unbalance and Accusine voltage imbalance) are different. If you want to know more details, please contact me(sesa20601) by email or teams.
Link copied. Please paste this link to share this article on your social media post.
i found this https://www.se.com/us/en/faqs/FA361943/
you will get a alarm event when voltage imbalance exceed 8%
Link copied. Please paste this link to share this article on your social media post.
The calculation methods for these two values(power supply voltage unbalance and Accusine voltage imbalance) are different. If you want to know more details, please contact me(sesa20601) by email or teams.