Accusine PCS+ CT connection

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • Accusine PCS+ CT connection
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Picard Charles_Murison Picard
488
Ramasamy_N
Captain Ramasamy_N Captain
113
Robert_Lee
Admiral Robert_Lee Admiral
92
Mehran_Mehrnia
Captain Mehran_Mehrnia Captain
89
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Solved
Mannguyen
Lieutenant | EcoXpert Master Mannguyen Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master

Posted: ‎2024-09-09 02:02 AM

0 Likes
7
1772
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-09-09 02:02 AM

Accusine PCS+ CT connection

Hi all,

I'm trying to connect an Accusine PCS+ [model number] to a system where the Capacitor bank bus/Generator bus CT is applied together with the main bus CT, as shown in the attached diagram.

Do I need a summation CT at the interconnection point (marked in red) or can I connect directly to the Accusine's CT terminal port?

Could you please provide a connection diagram with your recommendations?

Thank you for your help.

Attachments
Labels
  • Labels:
  • Power Quality
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Remi_Bolduc
Lieutenant JG Remi_Bolduc Lieutenant JG
Lieutenant JG

Posted: ‎2024-09-17 05:50 AM

1 Like
1
1620
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-09-17 05:50 AM

Hi all, You will need summation CT's if you can operate in co-generation, however if you the gen set is a back up source of power, then you don't. However the current vector summation should be completed on an external terminal block, especially that you have a capacitor bank in the circuit. Keep in mind that CT polarity most be respected and all the CT's must have the same ratio. For optimized performance, it's always recommended to have CT's at the capacitor bank feeder even if the capacitor bank have tuning reactors.

See Answer In Context

Reply
Replies 7
caimin_pan
Lieutenant JG caimin_pan Lieutenant JG
Lieutenant JG

Posted: ‎2024-09-09 10:18 PM

1 Like
2
1739
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-09-09 10:18 PM

 You don't need a summation CT at the interconnection point. But the capacitor bank must be equipped with reactors to avoid amplifying harmonics and affecting the performance of PCS+.

Reply
Mannguyen
Lieutenant | EcoXpert Master Mannguyen Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master

Posted: ‎2024-09-10 11:33 PM

0 Likes
1
1711
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-09-10 11:33 PM

@caimin_pan The summation CT is not necessary is clear, but the reactors to be equipped with the capacitor bank to protect PCS+ cannot be included in the AHF offers, due to the complexity of sizing and calculating reactors based on the existing electrical system and impact on the price. Please advise the solution. Thanks again.

Reply
caimin_pan
Lieutenant JG caimin_pan Lieutenant JG
Lieutenant JG

Posted: ‎2024-09-11 12:08 AM

0 Likes
0
1703
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-09-11 12:08 AM

The combination of capacitors and series reactors is necessary for power systems with harmonics, not just for protecting PCSP. The reactors (14% or 7%) are equipped with the capacitor bank , 14% reactor avoid amplifying harmonics of the 3th or higher order, 7% reactor avoid amplifying harmonics of the 5th or higher order. 

Reply
Mannguyen
Lieutenant | EcoXpert Master Mannguyen Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master

Posted: ‎2024-09-16 12:01 AM

0 Likes
0
1644
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-09-16 12:01 AM

Dear all,

Continuing with the CT connection method in combination with cases of the main bus CT and Cap. bank CT.

The image attached is a recommended diagram from FSSE for the CTs connection for PCS+, please help me with the parallel connection of the Main bus CT and Cap. bank CT whether it works or not? and advise if there is a proper way to combine these CTs into PCS+.

Thank you all in advance.

Attachments
Reply
Remi_Bolduc
Lieutenant JG Remi_Bolduc Lieutenant JG
Lieutenant JG

Posted: ‎2024-09-17 05:50 AM

1 Like
1
1621
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-09-17 05:50 AM

Hi all, You will need summation CT's if you can operate in co-generation, however if you the gen set is a back up source of power, then you don't. However the current vector summation should be completed on an external terminal block, especially that you have a capacitor bank in the circuit. Keep in mind that CT polarity most be respected and all the CT's must have the same ratio. For optimized performance, it's always recommended to have CT's at the capacitor bank feeder even if the capacitor bank have tuning reactors.

Reply
Mannguyen
Lieutenant | EcoXpert Master Mannguyen Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master

Posted: ‎2024-09-17 09:33 PM

0 Likes
0
1608
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-09-17 09:33 PM

We installed some PCS+s to the customers with existing Cap. bank and we applied the CT summation for the combination of CTs into PCS+ with no issue, an SE field Services staff recently recommended that no need for the CT summation for the Main Incoming Bus CT and Cap. Bank CT connection as the attached diagram. However we are concerned about the paralleling connection of two separated CT sets, please advise if this type of CT connection has some drawbacks or disadvantages compared with the CT summation application.
Thank you in advance.

Attachments
Reply
Remi_Bolduc
Lieutenant JG Remi_Bolduc Lieutenant JG
Lieutenant JG

Posted: ‎2024-09-19 05:40 AM

0 Likes
0
1572
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-09-19 05:40 AM

CT polarity on the primary side are fine. On the secondary for each CT on the same phase, make sure that all the X1 are together and all the X2 are together. Again, standard capacitor bank are not recommended in this type of application, the harmonic mitigation performance may be diminished. 

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login