ATHDF% or THDFi or current THD

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • ATHDF% or THDFi or current THD
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Picard Charles_Murison Picard
477
Ramasamy_N
Captain Ramasamy_N Captain
113
Robert_Lee
Admiral Robert_Lee Admiral
92
Mehran_Mehrnia
Captain Mehran_Mehrnia Captain
85
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Solved
Kendal
Kendal
Cadet

Posted: ‎2022-12-13 05:46 AM . Last Modified: ‎2022-12-13 05:49 AM

0 Likes
2
1135
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-12-13 05:46 AM

ATHDF% or THDFi or current THD

Hi,

 

Can someone explain to me how bad this figure is for ATHDF%...using a Tektronix power meter PA1000 to characterise a power adapter 230VAC to 5Vdc. The power adapter has a rating of 5V output, max 1A. When loaded at max 1A, the power meter provides a power factor reading of 0.427 and ATHDF% of 154. I'm having difficulty interpreting 154 for THDF(current). 154% looks bad but is it normal for these cheap type switching PSUs? At 25% load or 250mA the reading increases to 163%.

 

Thanks

Labels
  • Labels:
  • Power Quality
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DanL
Captain DanL Captain
Captain

Posted: ‎2022-12-13 02:27 PM

2 Likes
1
1121
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-12-13 02:27 PM

I'm not familiar with the term "ATHDF%" nor the "Tektronix power meter PA1000", but if I had to guess this is the "Amps Total Harmonic Distortion as a % of Fundamental".
Yes, >100% current distortion as a % of fundamental is very typical for all switch-mode power supplies without active PFC. Normally for most loads <50W, load current THD is not a concern.

See Answer In Context

Reply
Replies 2
DanL
Captain DanL Captain
Captain

Posted: ‎2022-12-13 02:27 PM

2 Likes
1
1122
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-12-13 02:27 PM

I'm not familiar with the term "ATHDF%" nor the "Tektronix power meter PA1000", but if I had to guess this is the "Amps Total Harmonic Distortion as a % of Fundamental".
Yes, >100% current distortion as a % of fundamental is very typical for all switch-mode power supplies without active PFC. Normally for most loads <50W, load current THD is not a concern.

Reply
Kendal
Kendal
Cadet

Posted: ‎2022-12-14 02:09 AM

0 Likes
0
1111
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-12-14 02:09 AM

Great, thanks for the reply. Yes, your guess of the acronym ATHDF% is correct.

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of