Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation
Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively. Register now to secure your spot!
Metering & Power Quality
Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.
Posted: 2016-10-19 01:44 AM
Link copied. Please paste this link to share this article on your social media post.
Hi,
Does anybody know what the minimum voltage that the 7550RTU can take on a digital input from a pulse meter ?
The manual states external supply of maximum 130VDC but what is the minimum for the input to operate correctly ?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
The ION7550 digital inputs are internally excited to -30Vdc with a high-impedance source making them most suitable for simple closed-contact sensing (zero volts).
Any (low-impedance) voltage source connected between 0V and 130V will be recognized as closed.
Hope this helps
Dan
Link copied. Please paste this link to share this article on your social media post.
Hi Richard,
Dan Loewen has provided a good description which should answer your question.
Nonetheless, here is a picture in case it is still not clear:
Kind Regards,
Chris.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.
With achievable small steps, users progress and continually feel satisfaction in task accomplishment.
Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.
of