TM172E28R analog outputs 4-20mA configuration
Hi Guys,
I'm trying to configure the Analog outputs (AO1,AO2) of TM172E28R expansion module to 4-20mA output (current modulation) but having problems with it.
I've configure both AO1 and AO2 as value '0' (current modulation) under Advanced Settings.
And then I do the full download. Everything complies fine with no error but when I test the outputs with a multimeter both outputs are showing around 40-50mA no matter what the programming value being 0-1000.
If I measure the AO3 and AO4 of the main controller, it correctly shows value within 4-20mA.
What am I doing wrong here?
- Labels:
-
HVAC
- Tags:
- english
Link copied. Please paste this link to share this article on your social media post.
Accepted Solutions
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-01-24 02:57 AM
Hi,
Have you done a download all and reboot of the PLC?
Configuration is sent to expansions during the PLC boot phase.
If you have a TM171ADMI, you can disconnect the CAN bus and connect directly to the expansion using ESME HVAC Installer and TM171ADMI. Once connected you can verify the I/O settings and manually test them.
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-01-24 02:57 AM
Hi,
Have you done a download all and reboot of the PLC?
Configuration is sent to expansions during the PLC boot phase.
If you have a TM171ADMI, you can disconnect the CAN bus and connect directly to the expansion using ESME HVAC Installer and TM171ADMI. Once connected you can verify the I/O settings and manually test them.