Simulating LMC058 controller with ethernet port in soMachine software

Machine Automation Forum

A forum addressing machine automation solutions for the complete machine lifecycle. Including offers like Machine Advisor, Modicon PLC/PacDrive, Lexium or Preventa. Discuss and share knowledge on offers relating to cloud-based service platforms, machine localization and monitoring, industrial operations control, motion products as well as safety function!

Solved
jerryvdk
Crewman
Crewman
0 Likes
1
771

Simulating LMC058 controller with ethernet port in soMachine software

Hi all,

 

Is it possible to simulate LMC058 PLC with ethernet in soMachine software. I want to test the logic written in PLC which uses tcpudp library.

 

 

Tags (1)

Accepted Solutions
SimA
Ensign Ensign
Ensign

Re: Simulating LMC058 controller with ethernet port in soMachine software

Unfortunately, some functions/libraries that are linked to hardware communication ports cannot be simulated without a controller.  You can simulate the SoMachine / Machine Expert protocol to simularte HMI/Scada communication but you can't simulate raw tcp/udp from the TcpUdpCommunication library. 

 

You will need a physical controller to test you tcp udp communication.  If you don't have a LMC058, you could test that part on a M258, M241 or M251.

See Answer In Context

Tags (1)
1 Reply 1
SimA
Ensign Ensign
Ensign

Re: Simulating LMC058 controller with ethernet port in soMachine software

Unfortunately, some functions/libraries that are linked to hardware communication ports cannot be simulated without a controller.  You can simulate the SoMachine / Machine Expert protocol to simularte HMI/Scada communication but you can't simulate raw tcp/udp from the TcpUdpCommunication library. 

 

You will need a physical controller to test you tcp udp communication.  If you don't have a LMC058, you could test that part on a M258, M241 or M251.