Launch of Consumer/Home Owner registration process! We are pleased to announce the commencement of the Consumer/Home Owner Registration Process on Community. Consumers/Home Owners may now proceed to register by clicking on Login/Register. The process is straightforward and designed to be completed in just a few steps.
Support Forum for HVAC and pumping machines, Modicon M17x and EcoStruxure Machine Expert HVAC software for chillers, AHU, CRAC units for datacenters or process chillers applications - from design, implementation to troubleshooting and more, by Schneider Electric.
Search in
Posted: 2021-07-26 02:40 AM . Last Modified: 2021-07-26 03:46 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-26 02:40 AM . Last Modified: 2021-07-26 03:46 AM
Hi,
We are using LMC078 motion controller in our project to control 12 motors simultaneously. Softmotion encoder will act as master for all the axis.
We created softMotion encoder under IME_EncIn in device tree and created a logic drive under that. Please see the image. Also find the logical encoder page.
In our motion sequence, we enable camming between logical encoder master axis and a physical axis. In the sequence encoder master will move forward, will reset the master axis position via MC_SetPosition.(We tried using MC_Home function block, but that was not working). We are setting the position to zero. But what we can see that even the position of encoder is resetting to 0, we can see at some point of time, encoder overflows as seen in the video.
Since the slave axis is engaged to master axis, when suddenly the position of the actual position changes to a negative value all the slave suddenly stops and try to match with the new position change which will create a sudden stop and whole machine jerks.
What we observe is that even the factPosition changes when we call MC_setPosition to 0, some of the internal variables in softMotionEncoder is not changing(dwActPosition...) because of which factPosition overflows at some point of time.
We are surprised that this is happening in LMC078 PLC and is not visible in the competitors motion controller PLC's. Is there any work around for this. This looks like a bug in the PLC/codesys firmware!.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-08-04 04:04 AM
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document