How Many elements per page within the HMI of a TM172DCLxxx.

Machine Automation Forum

A forum addressing machine automation solutions for the complete machine lifecycle. Including offers like Machine Advisor, Modicon PLC/PacDrive, Lexium or Preventa. Discuss and share knowledge on offers relating to cloud-based service platforms, machine localization and monitoring, industrial operations control, motion products as well as safety function!

Solved
sardila
Ensign
Ensign
0 Likes
2
822

How Many elements per page within the HMI of a TM172DCLxxx.

Hi, 

 

I created a page to show fault history. In total, I have 10 Alarm alerts with a timestamp, which means 40 edit fields. But when I compile the program, I got an error:

 

=> Page Contains too many elements. 


--- Start compilation (PreBuild) 1:57:33 PM ---
Generating IEC code for HMI...
ERROR generating IEC code for HMI

 

I removed them until I could compile them successfully. The total number of element I have on the screen is 32 edit fields. I haven't found any document where refers to maximum elements per page.

 

Does anyone know about this issue??

 

 

Thanks in advance!

 

 

Tags (1)

Accepted Solutions
Bastian_Schmitz
Commander Commander
Commander
0 Likes
1
819

Re: How Many elements per page within the HMI of a TM172DCLxxx.

To reduce the number of objects and to increase the number of possible alarm entry you can use a dynamic set list. In the attached PDF could you see how it works.

See Answer In Context

Attachments
Tags (3)
2 Replies 2
Bastian_Schmitz
Commander Commander
Commander
0 Likes
1
820

Re: How Many elements per page within the HMI of a TM172DCLxxx.

To reduce the number of objects and to increase the number of possible alarm entry you can use a dynamic set list. In the attached PDF could you see how it works.

Attachments
Tags (3)
sardila
Ensign
Ensign
0 Likes
0
811

Re: How Many elements per page within the HMI of a TM172DCLxxx.

Thanks for your help. I could handle the navigation between pages and uses sets to manage the information displayed.

Tags (1)