Hi all,
I've unsuccessfully been trying to use RETAIN variables within the HMI of a TM172DCLxxx.
Previously, I have tried to create them and tie them to buttons, resulting in the following error;
error G0096: RTN_XAUTORECOVERPOWER => Init value object not found
This variable previously worked when it was not a RETAIN type, hence scope was correct and no spelling issues. The HMI Properties window also automatically recognised the type, so it was actually finding the variable.
I further tried to define some without assigning to buttons; producing a total of three RETAIN variables, resulting in multiple of the following error type;
error A4100: RTN_USIARCONTROLMODE => Retentive vars space exhausted
Following this, I changed the type of two of them to standard variables to reduce the potential use of the retentive space, however the same error as above.
Am I missing something regarding their use?
Thanks,
Jack
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-03 10:37 PM
As far as I know, the TM172DCL display doesn't have "retain" memory area. The retain memory area would be an area that would be retained by the battery automatically without any user action.
However, the M172 family has was is called eeprom parameters. Those values are saved in flash memory. Because the way an eeprom chip works, there is a maximum of write operation in the life of an eeprom cell. It is around 100 000 write operation per memory cell. To preserve the life of an eeprom chip, the write to an eeprom parameter is not done automatically. It can be called from the program with the sysWritePar functions (one per data type, int, bool, etc). This function is smart and only actually writes to the memory cell if the actual value sent to the function is different then the actual value in the eeprom variable. This prevents a useless write operation to the memory.
Another way to write to an eeprom is from an HMI page. When an eeprom variable is mapped to a data entry object on a page, the value will be written to eeprom memory each time the value is changed by the user.
Hope it makes it a bit more clear how it works.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-03 10:51 PM
Ah ok, I didn't realise that normally they would retained via CMOS.
I was hoping to avoid the sysWrite method, as I'd have to have a status variable linked to Programming and the overhead you describe.
In the HMI editor, can I manage EEPROM Parameters in any scope? For example, page local procedures or using a message? Is this just a feature of the TM172DCLxxx?
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.
With achievable small steps, users progress and continually feel satisfaction in task accomplishment.
Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.
of