Error Generating USB Programming files

Machine Automation Forum

A forum addressing machine automation solutions for the complete machine lifecycle. Including offers like Machine Advisor, Modicon PLC/PacDrive, Lexium or Preventa. Discuss and share knowledge on offers relating to cloud-based service platforms, machine localization and monitoring, industrial operations control, motion products as well as safety function!

Solved
sardila
Ensign
Ensign
0 Likes
3
320

Error Generating USB Programming files

Hi,

 

I recently Updated the EcoStruxture Machine Expert  version to the latest one 1.4.0 and the target bios to 668.12 firmware version.

 

Now, I am getting errors traying to generate the USB programming files:

 

 

File C:\Users\sardila\Documents\repository\89r-cw-h-plc-code\USBCWH2020_7IO\PARAM.DAT and C:\Users\sardila\Documents\repository\89r-cw-h-plc-code\USBCWH2020_7IO\PARAM.RAW correctly generated
Error generating file C:\Users\sardila\Documents\repository\89r-cw-h-plc-code\USBCWH2020_7IO\PARAM.BIN
USB folder generated: C:\Users\sardila\Documents\repository\89r-cw-h-plc-code\USBCWH2020_7IO
File C:\Users\sardila\Documents\repository\89r-cw-h-plc-code\USBCWH2020_18IO\PARAM.DAT and C:\Users\sardila\Documents\repository\89r-cw-h-plc-code\USBCWH2020_18IO\PARAM.RAW correctly generated
Error generating file C:\Users\sardila\Documents\repository\89r-cw-h-plc-code\USBCWH2020_18IO\PARAM.BIN
USB folder generated: C:\Users\sardila\Documents\repository\89r-cw-h-plc-code\USBCWH2020_18IO

 

Anyone have had this issue before?

 

I much appreciate any suggestion, Thanks.

Tags (1)

Accepted Solutions
FedericoM
Lieutenant Lieutenant
Lieutenant
0 Likes
1
303

Re: Error Generating USB Programming files

Hello,

 

this is a known bug of version 1.4.0 with target 7/18 I/O.

 

You can fix it with the patch you can find at this link:

https://schneider-electric.box.com/s/svi3uam9raimwf51srhf70zv3idbup10

See Answer In Context

Tags (1)
3 Replies 3
Bastian_Schmitz
Commander Commander
Commander
0 Likes
0
309

Re: Error Generating USB Programming files

Hello,

If you update the target in a project and you get this error try the function "Refresh current target"

refresh.PNG

 

 

Tags (2)
FedericoM
Lieutenant Lieutenant
Lieutenant
0 Likes
1
304

Re: Error Generating USB Programming files

Hello,

 

this is a known bug of version 1.4.0 with target 7/18 I/O.

 

You can fix it with the patch you can find at this link:

https://schneider-electric.box.com/s/svi3uam9raimwf51srhf70zv3idbup10

Tags (1)
sardila
Ensign
Ensign
0 Likes
0
198

Re: Error Generating USB Programming files

Thanks, I much appreciated it.

 

The bug was fixed! 

Tags (1)