Welcome to the new Schneider Electric Community

It's your place to connect with experts and peers, get continuous support, and share knowledge.

  • Explore the new navigation for even easier access to your community.
  • Bookmark and use our new, easy-to-remember address (community.se.com).
  • Get ready for more content and an improved experience.

Contact SchneiderCommunity.Support@se.com if you have any questions.

Close
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
Send Invite Cancel
84690members
354052posts

Encoder postion overflow

Machine Automation Forum

A forum addressing machine automation solutions for the complete machine lifecycle. Including offers like Machine Advisor, Modicon PLC/PacDrive, Lexium or Preventa. Discuss and share knowledge on offers relating to cloud-based service platforms, machine localization and monitoring, industrial operations control, motion products as well as safety function!

jerryvdk
Crewman
Crewman

Encoder postion overflow

Hi,

 

We are using LMC078 motion controller in our project to control 12 motors simultaneously. Softmotion encoder will act as master for all the axis.

 

We created softMotion encoder under IME_EncIn in device tree and created a logic drive under that. Please see the image. Also find the logical encoder page.

 

In our motion sequence, we enable camming between logical encoder master axis and a physical axis. In the sequence encoder master will move forward, will reset the master axis position via MC_SetPosition.(We tried using MC_Home function block, but that was not working). We are setting the position to zero. But what we can see that even the position of encoder is resetting to 0, we can see at some point of time, encoder overflows as seen in the video. 

 

Since the slave axis is engaged to master axis, when suddenly the position of the actual position changes to a negative value all the slave suddenly stops and try to match with the new position change which will create a sudden stop and whole machine jerks.

 

What we observe is that even the factPosition changes when we call MC_setPosition to 0, some of the internal variables in softMotionEncoder is not changing(dwActPosition...) because of which factPosition overflows at some point of time.

 

We are surprised that this is happening in LMC078 PLC and is not visible in the competitors motion controller PLC's. Is there any work around for this. This looks like a bug in the PLC/codesys firmware!.LMC078EncoderView.pngLMC078LogicalEncoderSettings.png

 

 

Attachments
Tags (1)
1 Reply 1
jerryvdk
Crewman
Crewman

Re: Encoder postion overflow

Anybody faces similar issues?

Tags (1)