Welcome to the new Schneider Electric Community

It's your place to connect with experts and peers, get continuous support, and share knowledge.

  • Explore the new navigation for even easier access to your community.
  • Bookmark and use our new, easy-to-remember address (community.se.com).
  • Get ready for more content and an improved experience.

Contact SchneiderCommunity.Support@se.com if you have any questions.

Close
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
Send Invite Cancel
84398members
353588posts

BACnet Addons Library for Ecostruxure Machine Expert HVAC

Machine Automation Forum

A forum addressing machine automation solutions for the complete machine lifecycle. Including offers like Machine Advisor, Modicon PLC/PacDrive, Lexium or Preventa. Discuss and share knowledge on offers relating to cloud-based service platforms, machine localization and monitoring, industrial operations control, motion products as well as safety function!

Solved
Anawat
Lt. Commander
Lt. Commander
0 Likes
11
4594

BACnet Addons Library for Ecostruxure Machine Expert HVAC

I'm working on M172 controllers and need to use BACnet protocol.

 

Anybody know where can i download BACnet Addons Library for Ecostruxure Machine Expert HVAC?


Accepted Solutions
PierpaoloA
Schneider Alumni (Retired)
Schneider Alumni (Retired)
10
4586

Re: BACnet Addons Library for Ecostruxure Machine Expert HVAC

Hi, you can download the BACnet Addons library for ESME HVAC from this link: https://schneider-electric.box.com/s/7r58enj2e5wk3i08v37jyho5apsy445j

Please feel free to reach out for any question you might have in this regards.

Pierpaolo
----

Pierpaolo Armeli
Technical Expert Community Facilitator & HVAC Expert

See Answer In Context

Tags (1)
PierpaoloA
Schneider Alumni (Retired)
Schneider Alumni (Retired)
0 Likes
0
4489

Re: BACnet Addons Library for Ecostruxure Machine Expert HVAC

Hi Anawat,

 

As discussed, the best in this case is to use a workaround, as by using a mirror point and alarm object in EBO system.

 

Pier

See Answer In Context

Tags (1)
11 Replies 11
PierpaoloA
Schneider Alumni (Retired)
Schneider Alumni (Retired)
10
4587

Re: BACnet Addons Library for Ecostruxure Machine Expert HVAC

Hi, you can download the BACnet Addons library for ESME HVAC from this link: https://schneider-electric.box.com/s/7r58enj2e5wk3i08v37jyho5apsy445j

Please feel free to reach out for any question you might have in this regards.

Pierpaolo
----

Pierpaolo Armeli
Technical Expert Community Facilitator & HVAC Expert
Tags (1)
Anawat
Lt. Commander
Lt. Commander
0 Likes
0
4577

Re: BACnet Addons Library for Ecostruxure Machine Expert HVAC

@PierpaoloA 

 

Thank you very much.

Tags (1)
Anawat
Lt. Commander
Lt. Commander
0 Likes
4
4529

Re: BACnet Addons Library for Ecostruxure Machine Expert HVAC

Hi Pier,

 

I am able to discover MP172 BACnet device and objects into EBO. 

 

i have one issue about alarm and reset text Message of BI object. These are not propertied in ESME to add.

Tags (1)
PierpaoloA
Schneider Alumni (Retired)
Schneider Alumni (Retired)
0 Likes
3
4513

Re: BACnet Addons Library for Ecostruxure Machine Expert HVAC

Hi,

 

the string fields can be edited only from the PLC (they are read-only)

 

You can double check on the PICS which properties are implemented (https://www.bacnetinternational.net/btl/index.php?m=266) - they are in line with the AAC profile.

 

Please contact me directly to investigate further and then we can report here the findings.

 

Thank you.

Tags (1)
Anawat
Lt. Commander
Lt. Commander
0 Likes
0
4507

Re: BACnet Addons Library for Ecostruxure Machine Expert HVAC

I got it. Thank you.

Tags (1)
PierpaoloA
Schneider Alumni (Retired)
Schneider Alumni (Retired)
0 Likes
0
4488

Re: BACnet Addons Library for Ecostruxure Machine Expert HVAC

 
PierpaoloA
Schneider Alumni (Retired)
Schneider Alumni (Retired)
0 Likes
0
4490

Re: BACnet Addons Library for Ecostruxure Machine Expert HVAC

Hi Anawat,

 

As discussed, the best in this case is to use a workaround, as by using a mirror point and alarm object in EBO system.

 

Pier

Tags (1)
VaidasM
Ensign
Ensign
0 Likes
1
1666

Re: BACnet Addons Library for Ecostruxure Machine Expert HVAC

Hello, 

 

we are using Bacnet Library 2.3 version within M172 controllers for AHU application and we experience random disconnections from the network. We've moved Bacnet task from background to timed task (we believe their priority is higher), also made longer timeouts on Bacnet line in AS-P, situation got a lot better, but not perfect - disconnections still occurs. Do you have any ideas ?

 

Thank you.

Tags (1)
Anawat
Lt. Commander
Lt. Commander
0 Likes
0
1621

Re: BACnet Addons Library for Ecostruxure Machine Expert HVAC

I'm not found this error before. You can try to check the below link. It might be help.

 

Schneider M172 PLC and AS-P BACnet communication problem.

Tags (1)
jf_graphen_pl_b
Ensign
Ensign
0 Likes
1
287

Re: BACnet Addons Library for Ecostruxure Machine Expert HVAC

Hello Pierpaolo,

 

I 've the same kindly request but concerning  Modbus. Would you like to send  al link to MODBUS Addons Library for Ecostruxure Machine Expert HVAC?

 

Thanking in advance,

Artur

Tags (1)
Ismet_S
Ensign Ensign
Ensign
0 Likes
0
223

Modbus Addons Library for Ecostruxure Machine Expert HVAC

Hi,

 

By default the Modbus Addon "ModBUS_Addons_M172P_O.plclib" is under the folder :

 

"C:\Program Files (x86)\Schneider Electric\EcoStruxureMachineExpertHVAC\Catalog\FreeAdvance\PLC"

 

BR

Tags (1)