Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

bCX gets ping response but is offline in WebPage and Continuum

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • bCX gets ping response but is offline in WebPage and Continuum
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Dave_Shore
    Dave_Shore
  • DavidFisher
    DavidFisher
  • Product_Support
    Product_Support
  • DavidChild
    DavidChild
  • Jonathan
    Jonathan
  • AdamSteele
    AdamSteele
  • CraigEl
    CraigEl
  • Sacco
    Sacco

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
4651 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

bCX gets ping response but is offline in WebPage and Continuum

Picard Product_Support
‎2018-09-09 11:50 PM

Last Updated: Administrator CraigEl Administrator ‎2022-08-08 03:44 AM

Issue

Cannot bring controller online in Continuum even though all settings are correct. Unable to browse to that controllers configuration webpage but can ping the controller. CPU LED blinking approximately two times a second (2 Hz at 50% duty).

Product Line

Andover Continuum

Environment

  • bCX40xx
  • bCX96xx
  • b3xxx
  • i2xxx

Cause

The controller is in bootloader mode and has lost its application program.

Resolution

If the bCX is in bootloader mode, with the CPU LED blinking approximately two times a second (2 Hz at 50% duty), then there are a couple things you can try to do to get the controller back online before sending it back for repair.

Basically it has lost its application program and dropped into bootloader mode. Try to uprev the controller with its application firmware to see if that will bring it back online.

  1. Attempt to uprev (Update OS) the controller from its device object in Continuum even though it may not show as online.
  2. Alternatively uprev the controller using the RoamIO to send the application firmware to the controller.

If neither of these options work the controller must be returned to be repaired through your normal RA procedure for your region. (this option may no longer be available, due to the age of the controller)

Note:

  1. An error code including 6818(hex) (c2026818 has been seen) or 26648(dec) during an attempted download or on a graphic.
    Example1:
    Q.E.Hosp Controller Download Error.jpg
    Example 2:
    Q.E.Hosp Controller Graphic error.jpg
  2. See a Quick time movie to indicate CPU light modes for controllers that shows the various stages of the CPU LED blink rate.
Labels (1)
Labels:
  • Andover Continuum
Tags (7)
  • Find more articles tagged with:
  • 5414
  • blind
  • DavidShore20
  • flash
  • light
  • red
  • rx
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore