Range of Wiegand Card Numbers and Site Codes for use with Continuum
  • Range of Wiegand Card Numbers and Site Codes for use with Continuum
  • CraigEl
    CraigEl
  • PaulFr
    PaulFr
  • Dave_Shore
    Dave_Shore
‎2018-09-09 11:57 PM
Last Updated: Administrator CraigEl Administrator ‎2022-08-08 05:55 PM
Continuum supports different Wiegand card formats and Custom formats, what is the largest card number that can be used?
Andover Continuum
  • ACX57xx (ACX5740, ACX5720)
  • AC1, AC1-A, AC1 Plus
  • ACX780, ACX700
  • Custom Wiegand - AccessFormat Array
  • Corporate 1000, 26 bit, 32 bit, 37 bit.
When ordering access cards and configuring personnel you need to know the maximum numbers allowed.
When configuring a Personnel object the maximum card number that can be entered is 4,294,967,295 the largest 32 bit number.
This is the largest possible card number when working with Custom Wiegand.
The maximum site code that can be used is 65,535 the largest 16 bit number.
Other Wiegand formats:
Continuum 37 bit: (Also known as Infinity 37)
Card number range: 1 - 524,287.  Site Code range: 1 - 4,095
Note: This is a proprietary format and further format details are not available.
Continuum 32 Bit (old format, not recommended for new sites):
Card number range: 1 - 8,191.  Site Code range: 1 - 2,047
26 Bit open standard:
Card number range: 1 - 65,535. Site Code range: 1 - 255
Corporate 1000 standard:
Card number range: 1 - 1,048,575. Site Code range: 1 - 4,095
NOTE
For custom formats the maximum format must not exceed 64-bits (i.e. start/end bit of the site code, card number, etc.)
See Which HID card formats are supported by Continuum?.
Tags (2)
  • 5587
  • infinity37